This is a very large motor to be operating off a residential service, if this is what you intend to do.
At 240v you will need a 100amp service to feed it. On acceleration & decel, these motors pull alot more current than the normal rated.
And you would also need to allow for the very large RPC to accommodate it.
You will need to ensure proper wire sizing on the feeder to avoid voltage drop.
The drive is most likely 3 phase SCR which poses problems with using an RPC due to keeping the phases balanced, with a PWM/IGBT drive with a DC power supply may be slightly better.
If this is in a industrial building, then you should have access to 3 phase.
I would be leery at using it residentially.