Check dgn48.4 for turret index start output which turn on bestact relay KR15(inside electrical cabinet) & solenoid valve YV81(mounted above index oil motor). Either KR17 & YV91 or KR18 & YV90 should turn on for rotational output.
dbstream,
On the bestact board, which ones are KR15, 17, and 18?
I have no electrical prints.
dgn48.4 does change.
KR15 is sixth "led" counting from the top. See attached
You need to check the physical output of the KR15. The led on the board is just the control voltage to turn on the relay. It's the relays that fail themselves. All timer descriptions are in the back of the ladder diagram.
Well I got it.
The timers where set to 00000000.
Neet, huh?
Thanks again for the help fellas! I appreciated it.
Heath