    Says if I don't connect them it will void my warranty.... Its a new $800 motor so I don't want to do that.

  2. #282
    Join Date
    Oct 2008
    Posts
    1645
    Your VFD is going to control the max aperage to that motor so it should not ever "overload".

    Right now your mainly using it via Keypad right?
    You will to get it going then you can do the External controls later.

    0-00 = 0
    Fill in all the motor Nameplate date in 0-01 to 0-05
    0-07 = Mains voltage = 220 or whatever it is there.

    Almost all the other defaults will work....
    1-00 = 0 Keypad
    1-01 = 0
    1-02 = 0
    1-03 = 0
    1-04 = 0
    1-05 = 0
    1-06 = 0 for Arrows or 1 for Pot on Keypad "01"
    1-07 = 1

    Section 2 all defaults
    Section 3
    3-00 = Max Freq you want example 120 = twice rated motor speed at 60 hz
    3-01 = Lowest Hz you want like 10 hz
    3.02 = 3
    3.03 = 1
    The rest of 3 can be defaults

    Section 4 you can set to what you want or leave alone
    Section 5 is not important until you interface to external control

    Perform Auto Tune as on page 4-53 in parameter group 14. Generally done with no belts or drive train hooked up. I just put my gear box in neutral to do it.

  3. #283
    Join Date
    Oct 2008
    Posts
    1645
    You do not need them but if you provide a link to the motor schematic and manual I *might* be able to tell you how to hook it up to the input of the VFD and you can set it as external fault to shut it down.


    Quote Originally Posted by eartaker View Post
    Says if I don't connect them it will void my warranty.... Its a new $800 motor so I don't want to do that.

  4. #284
    Join Date
    Apr 2007
    Posts
    2580

    Woah.....

    Please tell me you did not pay $800 for a motor for your $1500.00 milling machine... really? Hope you get that drive sorted right because I would be afraid to blow that thing up... peace

    Pete

  5. #285
    Join Date
    Aug 2009
    Posts
    899
    Awesome I went through the settings.

    The Schematic is here http://www.marathonelectric.com/CnxD...321892_365.pdf

  6. #286
    Join Date
    Aug 2009
    Posts
    899
    Pete,

    Lol no I paid $275 for it but its new and under Marathons warranty and from Marathon it is $800

  7. #287
    Join Date
    Aug 2009
    Posts
    899

  8. #288
    Join Date
    Oct 2008
    Posts
    1645
    They have several different types of protection and the best way to identify it is by the labels on those two wires. Are they P1 & P2 ?

  9. #289
    Join Date
    Oct 2008
    Posts
    1645
    Okay, P1 and P2 should be a normally closed circuit going thru three thermostatic protection switches.

    You can easily verify this by taking a ohm meter in continuity modem and checking between P1 and P2. You should have continuity.

    If so, what we need to do is wire this to your digital inputs on the VFD and then program that input as an External fault. Let me look at some more of the manual. Test those wires and let me know as well.

  10. #290
    Join Date
    Aug 2009
    Posts
    899
    rwskinner,

    yes it is p1 and p2

  11. #291
    Join Date
    Feb 2006
    Posts
    7063
    Thermal protection on motors typically consists of nothing more than a temperature-activated NC switch. It can be wired in series with any control signal that will cause the controller to shut down when the switch opens.

    Regards,
    Ray L.

  12. #292
    Join Date
    Oct 2008
    Posts
    1645
    Jeremy, are you using a contactor for the main power coming in?

    220 plug -> contactor -> VFD

    Switch controlling contactor?

  13. #293
    Join Date
    Aug 2009
    Posts
    899
    not at the moment. I just wired 220 directly to my VFD from my breaker box to test it out.

  14. #294
    Join Date
    Oct 2008
    Posts
    1645
    TECO Manual sucks!

    Before you do anything with P1 & P2 let's do a littel test.

    Program 5.08 = 1 for Stop and reset Freq to 0
    5.05 = 7 for ESD

    Now, see if the VFD runs or if it flashes ESD.

    Depending on how they have the ESD setup,
    It should be fail safe, which means S6 has to have 24v going to it to run, then when it the connection opens, it has an ESD shutdown.

    Please test the following.

    Test 1 - If it runs the way it is, while it's running, touch a jumper between S6 and 24V+ and see if it stops.

    Test 2
    If it flashes the ESD, then connect a jumper from S6 to 24v+, press reset, then run. Does it run?

    Let me know which way it operates and we can nail this down quick. Hopefully it's test 2.

    This is all chinese so there is no telling how they have the ESD logic.

  15. #295
    Join Date
    Oct 2008
    Posts
    1645
    Isn't that what I said? Right now, we are trying to figure out if Teco has a fail safe ESD like normal folk or if the have a fail closed system.

    If he had a contactor, it could have been put in series with it and the contactor would open during an overheat. The Teco doesn't have an External Fault input like most others have. They do have a reset terminal though but we were looking for an external fault.

    Quote Originally Posted by HimyKabibble View Post
    Thermal protection on motors typically consists of nothing more than a temperature-activated NC switch. It can be wired in series with any control signal that will cause the controller to shut down when the switch opens.

    Regards,
    Ray L.

  16. #296
    Join Date
    Aug 2009
    Posts
    899
    It runs with the settings and then stops after I contact 24v to S6. and flashes ES until I remove the jumper.

  17. #297
    Join Date
    Oct 2008
    Posts
    1645
    As I thought, Ass backwards from any real industrial fail open ESD.

    There is a little switch on the bottom, switch it to NPN, then use a jumper from Ground to S6. Tell me what happens.

  18. #298
    Join Date
    Oct 2008
    Posts
    1645
    Jeremy, sorry I'm getting tired. Put the switch back where it was and program 5.05 to 29 and retry the test.

  19. #299
    Join Date
    Aug 2009
    Posts
    899
    After flipping the switch the terminals do nothing. I can start the motor without the jumper attached and when I jump it nothing happens.

  20. #300
    Join Date
    Aug 2009
    Posts
    899
    With the setting on 29 it will not start without jumping the 24V and S6

Page 15 of 29 5131415161725

Similar Threads

  1. advice needed
    By teamjnz in forum Haas Lathes
    Replies: 2
    Last Post: 05-20-2009, 11:19 PM
  2. Advice needed.
    By Terence E in forum Community Club House
    Replies: 0
    Last Post: 05-14-2009, 03:56 PM
  3. advice needed / to buy or not???
    By teamjnz in forum Uncategorised MetalWorking Machines
    Replies: 13
    Last Post: 08-27-2008, 02:48 PM
  4. advice needed
    By trubleshtr in forum CNC Machine Related Electronics
    Replies: 32
    Last Post: 04-22-2005, 02:48 AM
  5. Little advice needed
    By STUG in forum DIY CNC Router Table Machines
    Replies: 1
    Last Post: 01-26-2005, 02:11 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •