NA has split Phase supply 2 Hot wires which are 180 degrees apart, each Hot wire is only 120v for residential supply
they take turns at being the return wire ( Neutral )
Reminds me of the often used mid-term electrical exam question.
If 120v L1 circuits have a total load of 30amps.
The 120v L2 circuits have a total load of 15 amps, what is the total current in the shared neutral, and why?
Any Takers??