    VFD- WJ200-022sf wiring question

    Before I shower my garage with sparks, I wanted to make sure my electrician and I set the VFD up properly. I have the Hitachi WJ200-002sf that calls for L1 - N - and chassis ground. I had the electrian install essentially a dryer plug, with L1 - L2 and the Ground. I intended to place L1 to either line, N to the additional Line and Ground as stated. Before I blow this beautiful VFD into the next state, is this correct or do I need to call the electrician again and fix my mistake. Thank you for your time!

    Edit - Realizing that this problem was well documented in http://www.cnczone.com/forums/phase-...ower-help.html so I am going to go grab a bite to eat and follow those instructions unless someone stops me in the forum beforehand. Sorry if I wasted anyones time. I love this forum and my CNC machine wouldn't exist without it!

  2. #2
    Join Date
    Dec 2013
    Posts
    5716

    Re: VFD- WJ200-022sf wiring question

    According to my manual, page 2-18, you have it correct.

  3. #3
    Join Date
    Feb 2013
    Posts
    7

    Talking Re: VFD- WJ200-022sf wiring question

    I really appreciate the quick response. It's wired and I flipped the breaker to find its fan turns on and its ready for greatness. I hope turning it on and off via the breaker won't harm it in the long term but, again, thank you and mission success!!!!

  4. #4
    Join Date
    Dec 2013
    Posts
    5716

    Re: VFD- WJ200-022sf wiring question

    My Pleasure !

    Turning it on and off from the breaker won't hurt a thing.

  5. #5
    Join Date
    Dec 2016
    Posts
    10

    Re: VFD- WJ200-022sf wiring question

    you can visit our website to see wiring drawing help you connect wires. VC680 spindle inverter wiring drawing-Blog-iNVOEE,CNC Spindle VFD,CNC Special Inverter Manufacturer in China

  6. #6
    Join Date
    Jan 2005
    Posts
    15362

    Re: VFD- WJ200-022sf wiring question

    Quote Originally Posted by JustinABobbitt View Post
    I really appreciate the quick response. It's wired and I flipped the breaker to find its fan turns on and its ready for greatness. I hope turning it on and off via the breaker won't harm it in the long term but, again, thank you and mission success!!!!
    Turning it on and off from a Breaker is ok but not a good practice ,( depending on the quality of the Breaker also ) a regular Breaker does not like this also, a Breaker is not a switch, most have this in there manual, manufactures usually specify how much time between turning them on / off, doing this in to short a run time shortens the life of the VFD, only ever turn the VFD off if it is already shut down and not under load, ( driving a Motor )

    The run time before a shut down, manufactures' recommend a minimum of 15 minutes to 30 minutes between a shut down and start is normal
    Mactec54

  7. #7
    Join Date
    Dec 2003
    Posts
    24220

    Re: VFD- WJ200-022sf wiring question

    Just about all of the VFD's I have installed recommend a contactor on the input supply in order to comply with motive power removal on E-stop, but all recommend that the contactor Not be used to stop start the VFD but used only in the case of emergency removal of power. Another option would be to use a aux contact on the contactor to input the VFD E-stop input.
    There is also a cautionary note in the WJ200 manual (xi) that covers the instances of what can occur if power failure during operation, especially if fed from a different source than the controller and VFD power is suddenly restored, it can cause continuation of motor operation..

    One other advantage of the Hitachi and other high end VFD's, is the option of making the 24vdc PLC or inputs sink or source.
    This enables BOB's or other controllers that have solid state open collector outputs to be able to be input to the VFD directly, without the necessity of a relay.
    The Huanyang has inputs for sinking BOB's only etc such as the Gecko type G540 etc.which are open drain Mosfet.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  8. #8
    Join Date
    Jan 2005
    Posts
    15362

    Re: VFD- WJ200-022sf wiring question

    Quote Originally Posted by Al_The_Man View Post
    Just about all of the VFD's I have installed recommend a contactor on the input supply in order to comply with motive power removal on E-stop, but all recommend that the contactor Not be used to stop start the VFD but used only in the case of emergency removal of power. Another option would be to use a aux contact on the contactor to input the VFD E-stop input.
    There is also a cautionary note in the WJ200 manual (xi) that covers the instances of what can occur if power failure during operation, especially if fed from a different source than the controller and VFD power is suddenly restored, it can cause continuation of motor operation..

    One other advantage of the Hitachi and other high end VFD's, is the option of making the 24vdc PLC or inputs sink or source.
    This enables BOB's or other controllers that have solid state open collector outputs to be able to be input to the VFD directly, without the necessity of a relay.
    The Huanyang has inputs for sinking BOB's only etc such as the Gecko type G540 etc.which are open drain Mosfet.
    Al.
    I agree with what you have posted, but you should know that there are very few Hobby guys that are doing this with there home build machines

    Most would not even have a clue as to what you have posted, even with there manuals in front of them, that show diagrams of how it should be done

    Not many even get close to how it should be done
    Mactec54

  9. #9
    Join Date
    Dec 2003
    Posts
    24220

    Re: VFD- WJ200-022sf wiring question

    The idea of this forum is to educate, I see no point denying those that are interested in furthering their education, I think you are doing a vast number an injustice by painting them with a broad brush..
    There are many many posts on this forum on the subject of building electronic components and educating the neophyte.
    In fact the site Automation Direct which tend to cater to the Hobbyist put out a paper on the subject I touched on.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Similar Threads

  1. WJ200-022sf and 2.2kw Spindle settings
    By Jmhx2 in forum Spindles / VFD
    Replies: 20
    Last Post: 04-15-2020, 01:13 AM
  2. VFD Hitachi WJ200-022SF control box?
    By ballistic42 in forum Spindles / VFD
    Replies: 12
    Last Post: 04-24-2016, 05:06 AM
  3. WTB: VFD HITACHI WJ200-022SF New/Used
    By Contract_Pilot in forum Want To Buy...Need help!
    Replies: 3
    Last Post: 08-28-2015, 09:48 PM
  4. WJ200 wiring main power in. Help
    By standles in forum Phase Converters
    Replies: 26
    Last Post: 10-10-2014, 01:04 PM
  5. Another sPID, G540, and Mach wiring question for the wiring challenged..
    By adam_m in forum DIY CNC Router Table Machines
    Replies: 17
    Last Post: 01-02-2014, 01:29 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •