Just about all of the VFD's I have installed recommend a contactor on the input supply in order to comply with motive power removal on E-stop, but all recommend that the contactor Not be used to stop start the VFD but used only in the case of emergency removal of power. Another option would be to use a aux contact on the contactor to input the VFD E-stop input.
There is also a cautionary note in the WJ200 manual (xi) that covers the instances of what can occur if power failure during operation, especially if fed from a different source than the controller and VFD power is suddenly restored, it can cause continuation of motor operation..
One other advantage of the Hitachi and other high end VFD's, is the option of making the 24vdc PLC or inputs sink or source.
This enables BOB's or other controllers that have solid state open collector outputs to be able to be input to the VFD directly, without the necessity of a relay.
The Huanyang has inputs for sinking BOB's only etc such as the Gecko type G540 etc.which are open drain Mosfet.