    Power Supply ground question

    My controller chassis houses my Gecko's, Bob Campbell breakout
    board, and solid state relays and all is grounded to earth ground
    from my 110ac line. The power supply however is in another
    chassis and the output is isolated from the imput, therefore
    when I connect the ground from the power supply to the
    Gecko's (term 1) it will not be connected to earth ground from
    the 110ac line. Will this cause a problem??

  2. #2
    Join Date
    Jul 2004
    Posts
    83
    I really want to power up my controller this weekend, and don't
    want to see a puff of smoke!!!
    I connected the (-) from the power supply to (term 1) of my
    Gecko's. I also connected the (-) from the power supply to
    my earth ground from the ac line.
    Please! Please! can anyone see a possible problem with this!
    Thanks
    Chas

  3. #3
    Join Date
    Dec 2003
    Posts
    24220
    Generally it is desirable to have all the power supply commons at ground potential and if the power supplies are all initially isolated it is considered safe to make them common ground, a test to see if commoning up will cause any significant problems is to do a test to see if doing so will cause a large leakage current to flow, measure the voltage both DC and AC from the supply common you wish to ground and the actual ground, you may see a voltage with a sensitive meter due to natural leakage, which is normal, while the meter is connected place a 100ohm resistor across the meter leads an see of any leakage voltage collapses, if it does, then you should be ok to common up.
    Al
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  4. #4
    Join Date
    Dec 2004
    Posts
    524
    Quote Originally Posted by Al_The_Man
    Generally it is desirable to have all the power supply commons at ground potential and if the power supplies are all initially isolated it is considered safe to make them common ground, a test to see if commoning up will cause any significant problems is to do a test to see if doing so will cause a large leakage current to flow, measure the voltage both DC and AC from the supply common you wish to ground and the actual ground, you may see a voltage with a sensitive meter due to natural leakage, which is normal, while the meter is connected place a 100ohm resistor across the meter leads an see of any leakage voltage collapses, if it does, then you should be ok to common up.
    Al
    Al, you left out the part that says: if the 100 ohm resistor vaporizes, it is NOT ok to common up.

    Ken
    Kenneth Lerman
    55 Main Street
    Newtown, CT 06470

  5. #5
    Join Date
    Dec 2003
    Posts
    24220
    Quote Originally Posted by lerman
    Al, you left out the part that says: if the 100 ohm resistor vaporizes, it is NOT ok to common up.
    Ken
    I took that as read...
    Actually, only 1 amp would flow if the difference was 110vac, but you would need a high wattage resistor to prevent vaporization :bat:
    Al
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  6. #6
    Join Date
    Oct 2004
    Posts
    742

    Grounding - Chas

    Did you get the e-mail I sent.
    Should answer questions.

    Good luck,
    Jerry

Similar Threads

  1. Good earth ground, what is your definition?
    By gar in forum CNC Machine Related Electronics
    Replies: 29
    Last Post: 06-16-2005, 03:22 AM
  2. Motor supply ground vs Logic ground?
    By Gashmore in forum CNC Machine Related Electronics
    Replies: 11
    Last Post: 06-07-2005, 11:21 PM
  3. Power Supply Question
    By BobLWeiss in forum Stepper Motors / Drives
    Replies: 13
    Last Post: 04-17-2005, 08:27 PM
  4. FNG Power Supply Question
    By SteinAir in forum DIY CNC Router Table Machines
    Replies: 0
    Last Post: 01-01-2005, 04:31 AM
  5. i got a power supply question
    By ljoe1969 in forum CNC Machine Related Electronics
    Replies: 21
    Last Post: 01-12-2004, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •