    Automatic Alternating 120v Switch???

    just got a new toy that will require an additional compressor. I only have 110 in my shop and the power is already stained.

    I'm trying to figure out how to prevent both compressors from at the same time. seems simple- relay that only allows one side to be open at a time then clicks OFF and when one of the two fires it blocks power to the other, then OFF then the second can fire.

    the plan is to have one for my general air and mist system, and one for my shiny new pneumatic spindle. the ideal would be to wire 220 and get a big compressor but thats not going to be cheap or realistic as this is a rental im planning on leaving in the next year or two. Plus its a duplex with a single drop split to both so amps are at a PREMIUM to say the least.

    all I have found are these but they seem to need a second switch to initiate the cycle.

    TWO COMPRESSORS, TWO SEPARATE AIR CIRCUITS its what I'm after, but I cant have them fire at the same time.

    lost. not great with electronics. HELP please.

  2. #2
    Join Date
    Dec 2003
    Posts
    24220
    Depends if you want it automatic or manual, but the easiest way I would think is to have a power relay for each with each having a N.C. aux contact.
    The aux contact would be wired in the circuit of the opposite contactor or relay coil.
    IOW, an electrical interlock.
    The other similar method is to pick up a reversing contactor off ebay, these have mechanical interlock as well as electrical.
    Using it this way it would obviously supply one of two motors rather than reverse one.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Dec 2010
    Posts
    1230
    Quote Originally Posted by Al_The_Man View Post
    Depends if you want it automatic or manual, but the easiest way I would think is to have a power relay for each with each having a N.C. aux contact.
    The aux contact would be wired in the circuit of the opposite contactor or relay coil.
    IOW, an electrical interlock.
    The other similar method is to pick up a reversing contactor off ebay, these have mechanical interlock as well as electrical.
    Using it this way it would obviously supply one of two motors rather than reverse one.
    Al.
    I'm afraid I cant quite picture it. wouldn't that require me to toggle them on?

    I'm wanting it completely automatic. they will be fighting each other to "fill" from a single outlet. both air circuits will be running simultaneously (one for the spindle, and one for mist coolant). I can't be involved in the switching process- I just need them to play nice and share ab outlet. otherwise I have to plug one into the breaker the cnc its on and I REALLY don't want to do that.

  4. #4
    Join Date
    Dec 2003
    Posts
    24220
    Well if automatic, something has to switch them at an appropriate time, what do you have in mind for this??
    What would be the sequence required?
    I understood you wanted one or the other running in order to avoid electrical O/L, what is this simultaneously running?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5
    Join Date
    Dec 2010
    Posts
    1230
    I keep going over it in my head then my head hurts. I'm thinking I might understand what you suggested though:

    wire a 120v relay with 120v switching N/C to the AC in on each one and wire the switch to the opposite compressor on the back side of the relay built into the compressor? that way when compressor 1 kicks on it cuts power to compressor 2. when compressor 1 fills it represses the relay on compressor 2 and when compressor 2 kicks on it kills power to compressor 1.

    right?

  6. #6
    Join Date
    Aug 2009
    Posts
    986
    I'm confused about why two compressors taking turns is going to be advantageous over a single compressor running full time. Is this just a duty cycle problem, where a single compressor would melt down if left running full time?

    How many cfm do you need total?

    I know nothing about the electronics side of this. I'm just curious about your goals.

  7. #7
    Join Date
    Dec 2003
    Posts
    24220
    It may not be quite that simple, but if using say one pressure switch off of one compressor, if it has a NO and a NC both with the same common, this would work if they are fed off of the same supply?
    The master N.O. would feed to the normal N.C. pressure switch of the slave.
    You would make one compressor the master, the other the slave, IOW the master would take precedence.
    In this instance the one you make the master, probably would be the one with the most demand.
    This method would require no other components.
    For any other options it may be wiser to use something like a Siemens smart relay, this way you will have more options when it comes to the required logic.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  8. #8
    Join Date
    Dec 2010
    Posts
    1230
    I need 6 cfm for the spindle (which is pushing the top end of what can be done on these small compressors) and ??? cfm for my kool mist. Just to run my spindle I will have to get a larger compressor (mine runs 4.5 cfm) and likely have to lower the PSI (thus slowing the spindle) to be able to keep up the air supply on the spindle alone.

    if I had 220 I would have to spend $600+ on a 5hp to keep up with both and have a 50% duty cycle. No way do I trust these compressors to run 1.5 hr strait very many times.

    this just seems like the only way to do it in my situation :-/

    swung by orvac on the way home and grabbed a few surplus 120v coil 10a @ 120vac relays for $10 ea. also picked up some anderson type connectors for the switching wires so I can move the compressors to drain.

    if this works I will be VERY grateful! can't see how it wouldn't though.

  9. #9
    Join Date
    Dec 2010
    Posts
    1230
    does this crappy hand drawing make any sense?

  10. #10
    Join Date
    Dec 2003
    Posts
    24220
    It would be clearer drawn in ladder logic, but I think you are going to get conflict if you do not make one compressor the master, the other the slave using simple logic.
    With the drawing you have to indicate which NC is tied to which relay?
    Check the compressors for existing relay and/or the type of pressure switch and contact configuration, if both N.O. and N.C and if they use the same common or are double pole?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  11. #11
    Join Date
    Dec 2010
    Posts
    1230
    gonna go cut for a while then I'll draw it in color.

    it should work fine (and easy actually). the simple explanation is that I am going to add a NC relay on the AC line to each compressor as a KILL SWITCH (KS). compressor 1 (C1) motor line is wired to trip KS on C2 and vise versa. So if C1 is running its sending power to KS on C2 so C2 has no power until C1 shuts off. Even if they both drop to 90psi at almost the same time whichever one gets there first gets the power and the other will kick on as soon as the first is done.

  12. #12
    Join Date
    Dec 2010
    Posts
    1230
    I hope this helps anyone understand that is thinking of doing something like this.

    First one shows two compressors plugged in normally and one is running.

    The second shows adding two NC relays to the AC line in to the compressor and using the power to the motor to OPEN the relay on the other compressor so it can not turn on.
    Attached Files Attached Files

  13. #13
    Join Date
    Feb 2011
    Posts
    110
    get this compressor when it goes on sale for 399 then you only need 1

    3.5 Horsepower, 60 Gallon, 130 PSI Vertical Air Compressor

  14. #14
    Join Date
    Dec 2010
    Posts
    1230
    Quote Originally Posted by kd4gij View Post
    get this compressor when it goes on sale for 399 then you only need 1

    3.5 Horsepower, 60 Gallon, 130 PSI Vertical Air Compressor
    Thats 240v. at this point it may be worth it to spend the extra $800 and week or two of lost work it will cost to run 240 and buy a 240v compressor

  15. #15
    Join Date
    Feb 2011
    Posts
    110
    That is about as small of compressor that will run the air spindale without running all the time. You are defantley need a 60 gallon tank. I have a 9 cfm 30gallon now and could only run a diegrinder 5 min then run out of air.added a 60 gallon tank to give 90gal tottle .it helped alot.

  16. #16
    Join Date
    Feb 2006
    Posts
    7063
    A large tank will not help any tool that requires a continuous, high airflow, like an air spindle, unless the compressor capacity, in terms of CFM at the tools required pressure, significantly exceeds the tool requirements. Otherwise, all you're doing is slightly delaying the time it takes for the tank to bleed down to where the compressor turns on the first time. After than it will still run continuously.

    Regards,
    Ray L.

  17. #17
    Join Date
    Dec 2003
    Posts
    24220
    Quote Originally Posted by PriddyShiddy View Post
    I hope this helps anyone understand that is thinking of doing something like this.
    I will whip up a drg today when time permits.
    BTW, you did not confirm the pressure switch details , are they N.O. and N.C. with the same common?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  18. #18
    Join Date
    Feb 2011
    Posts
    110
    Quote Originally Posted by HimyKabibble View Post
    A large tank will not help any tool that requires a continuous, high airflow, like an air spindle, unless the compressor capacity, in terms of CFM at the tools required pressure, significantly exceeds the tool requirements. Otherwise, all you're doing is slightly delaying the time it takes for the tank to bleed down to where the compressor turns on the first time. After than it will still run continuously.

    Regards,
    Ray L.
    I agree for 6 cfm spindle 12 cfm compressor min. to consider. the extra 60 gal only extend the use. I know I need a bigger conp. also

  19. #19
    Join Date
    Dec 2003
    Posts
    24220
    This should give a fairly simple solution, it allows turning on power from scratch, i.e. both comp ready to run, but one will take precedent, and also precedence will remain during operation.
    If comp switch has both N.O. and N.C. contact on the P.S. then top diagram should work without any other components.
    Otherwise bottom version with relay.
    I had to use a zip file as the DWG/DXF were too large.
    Al.
    Attached Files Attached Files
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  20. #20
    Join Date
    Dec 2010
    Posts
    1230
    Quote Originally Posted by Al_The_Man View Post
    I will whip up a drg today when time permits.
    BTW, you did not confirm the pressure switch details , are they N.O. and N.C. with the same common?
    Al.


    they are NO and would share a common, but I think I have been convinced not to waste my time on this. if for no other reason than the condensation the small compressor running wide open would create. I hadn't thought about that. the spindle needs CLEAN DRY air. I could fight as much as I want to dry it, but I would still have to run around draining the filters, traps and tanks so often it would be impractical.

    gonna see about getting a panel, wire, and outlets this weekend and start breaking some concrete. just a terribly poured walkway in the way. I'll break it at the seam, run PVC, wire a panel in the garage pulled right off the main breaker which is only 10' away from the garage. Then I can run the 240v to the attached shed and maybe insulate a little to knock out some noise.

    then I just have to wait to get a big compressor to be able to use my new spindle. Haste makes waste. I just wanted it ruining now, but jeopardizing its longevity with wet air isn't worth it.

Page 1 of 2 12

Similar Threads

  1. where can I buy 120V servo motors?
    By BiggerHammer in forum Servo Motors / Drives
    Replies: 3
    Last Post: 01-16-2010, 03:37 AM
  2. VFD 220V 120V & NOISE
    By JpBinc in forum CNC Machine Related Electronics
    Replies: 1
    Last Post: 11-10-2008, 05:17 AM
  3. Mazak QT15 with T32-B control does not switch to automatic mode
    By MarkusFunk in forum Mazak, Mitsubishi, Mazatrol
    Replies: 2
    Last Post: 06-06-2008, 03:54 AM
  4. Yet another 120v to 220v
    By Konstantin in forum CNC Machine Related Electronics
    Replies: 4
    Last Post: 02-24-2006, 08:57 PM
  5. 120V Stepper - how can it be driven?
    By andy_ck87028 in forum Stepper Motors / Drives
    Replies: 1
    Last Post: 07-17-2005, 09:16 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •