    Running an Air Compressor with a VFD.

    I have an air compressor with a 3ph 3hp motor. I bought the proper size VFD to power it. I really know nothing about programing the VFD. However, I wired it using the magnetic starter and it worked and motor stopped when to pressure(120psi) when I drained some air to 90psi it threw a code on the VFD. I reset VFD and it started just fine. I also wired the motor direct to the VFD and used the pressure switch running the wires to the GND and fwd terminals on the VFD as per a video on youtube. But the motor does not turn off at 120psi. So. Is there or What settings do I need to program in to the VFD?

  2. #2
    Join Date
    Jan 2005
    Posts
    15362

    Re: Running an Air Compressor with a VFD.

    Quote Originally Posted by TheDeon View Post
    I have an air compressor with a 3ph 3hp motor. I bought the proper size VFD to power it. I really know nothing about programing the VFD. However, I wired it using the magnetic starter and it worked and motor stopped when to pressure(120psi) when I drained some air to 90psi it threw a code on the VFD. I reset VFD and it started just fine. I also wired the motor direct to the VFD and used the pressure switch running the wires to the GND and fwd terminals on the VFD as per a video on youtube. But the motor does not turn off at 120psi. So. Is there or What settings do I need to program in to the VFD?
    Yes you will have to have Terminal control Parameter set, you did not say what VFD you have, there really is not much to program, for what you are doing, most VFD drives default to a standard AC motor
    Mactec54

  3. #3
    Join Date
    Dec 2003
    Posts
    24220

    Re: Running an Air Compressor with a VFD.

    It may pay to stick an unloader valve in the air line that allows the motor to come up to full rpm until going on line.
    The could be achieved with one of the outputs of the VFD set to Up-to-Speed.
    An unloader is often used in the case of larger compressors.
    Ensure you set the right pole count for the motor also, most are 4 pole motors.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  4. #4
    Join Date
    Dec 2016
    Posts
    27

    Re: Running an Air Compressor with a VFD.

    Thanks for your replys. HY04D023VFD. The air compressor does have an unloader valve. The video on youtube didn't specify any settings programmed into the VFD.

  5. #5
    Join Date
    Jan 2005
    Posts
    15362

    Re: Running an Air Compressor with a VFD.

    Quote Originally Posted by TheDeon View Post
    Thanks for your replys. HY04D023VFD. The air compressor does have an unloader valve. The video on youtube didn't specify any settings programmed into the VFD.
    Have you got a link to the video, the unloader pressure switch normally has high voltage across it, but if he is just using it as a switch then that should work on those connections

    What Parameters have you set
    Mactec54

  6. #6
    Join Date
    Dec 2016
    Posts
    27

    Re: Running an Air Compressor with a VFD.

    I have no link to the video. But search VFD running an air compressor. I'm not sure what parameters I should/could use and what to set them at. I have it set to 60hz as far as parameters go. Not sure about the rest of them. It starts up when I plug it in and push start on the VFD, It builds up to 120psi the air switch activates but doesn't communicate that to the VFD(even though it is wired to the FWD and GND terminals) like the video. I can turn it off manually and restart it manually with the VFD and it does just fine even with 120psi in the tank.

  7. #7
    Join Date
    Dec 2016
    Posts
    27

    Re: Running an Air Compressor with a VFD.

    Well I took some pictures of my manual and wrote down the setting on the VFD. But it ain't letting me find them to post them.

  8. #8
    Join Date
    Jan 2005
    Posts
    15362

    Re: Running an Air Compressor with a VFD.

    Quote Originally Posted by TheDeon View Post
    Well I took some pictures of my manual and wrote down the setting on the VFD. But it ain't letting me find them to post them.
    Ok here is all you need to set as you are using just a start / stop for your Compressor Motor, note there are no variables being used with these settings, meaning you are set at 60Hz and the motor rated speed

    You may have the Jumper like photos below, you may not, but if you have this you will need to change it

    Never Turn Your Compressor Off if it is Running, always Wait for it to Unload Before Turning it OFF

    Huanyang Mactec54

    60Hz AC Motor Compressor

    PD000=0 ( For Parameter unlock ( 1 ) for Parameter Lock )

    PD001=0 (1 For Remote Control)

    PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )

    ( J1 Also May Need to be set for Terminal Control )

    PD003=60

    PD004=60

    PD005=60

    PD007=10

    PD008=240 (Motor Rated Voltage )

    PD009=15

    PD010=8

    PD011=60

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014 Acceleration=12 ( Adjust to suit)

    PD015 Deceleration=12 (Adjust to suit)
    ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD141=240 ( Motor Rated Voltage )

    PD142= ( Motor Max Rated Amps)

    PD143=4 ( Motor Number of Poles)

    PD144= ( Max motor Speed ) ( 3000 Can be used )

    PD72=60

    PD73=60
    Mactec54

  9. #9
    Join Date
    Dec 2016
    Posts
    27

    Re: Running an Air Compressor with a VFD.

    Well I don't have a PD141 or higher then PD35. It goes from Pn1 thru Pn35. It only has 1 buss terminal row. 12v out, 5v out, 5v in, 10v in, 20mA in,5v Fout, GND, FWD, REV, RST, DO+, D1-, D2 Jog, Lk, Lb, Lz. I hope this helps. I'm not sure what to do.

  10. #10
    ericks Guest

    Re: Running an Air Compressor with a VFD.

    What is your motor's voltage?
    Also your motor's Kw?
    Is it possible to post an image of the motor "name plate"...?

  11. #11
    Join Date
    Dec 2003
    Posts
    24220

    Re: Running an Air Compressor with a VFD.

    PD050 -PD053 is to assign an output, you could wire a relay to one to switch the Unload valve and set for frequency reach .
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Similar Threads

  1. Air Compressor for PRO 408
    By nsbr in forum Shopsabre
    Replies: 1
    Last Post: 11-04-2017, 02:36 PM
  2. Y Axis + Slave not running together when running G-Code
    By Fierra in forum Mach Software (ArtSoft software)
    Replies: 2
    Last Post: 05-19-2017, 08:56 AM
  3. Running a 3 phase 208v compressor motor on 240v
    By awerby in forum Uncategorised MetalWorking Machines
    Replies: 5
    Last Post: 07-27-2014, 10:30 PM
  4. running emc as a simulator, running out of ideas
    By CaptainVee in forum LinuxCNC (formerly EMC2)
    Replies: 59
    Last Post: 10-13-2012, 10:52 PM
  5. Replies: 6
    Last Post: 07-23-2012, 03:39 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •