    New VF-2SS wiring question

    Well, my new machine has been sitting on my garage floor for roughly 30 minutes!

    I'm trying to get the thing wired today so I can have the techs come and do their thing before the weekend and Sellway is slow.

    Does this thing need a neutral going to the main cabinet? I can't find that information anywhere.

  2. #2
    Join Date
    Jul 2005
    Posts
    12177
    Quote Originally Posted by Matt@RFR View Post
    Well, my new machine has been sitting on my garage floor for roughly 30 minutes!

    I'm trying to get the thing wired today so I can have the techs come and do their thing before the weekend and Sellway is slow.

    Does this thing need a neutral going to the main cabinet? I can't find that information anywhere.
    No, just the three phases onto the terminal block above the main breaker. And a ground to the grounding terminal near them.

    The Haas machines do not use a neutral line.
    An open mind is a virtue...so long as all the common sense has not leaked out.

  3. #3
    Join Date
    Apr 2005
    Posts
    713
    What would I do without you Geof?! Thanks!

  4. #4
    Join Date
    Nov 2005
    Posts
    164
    Quick question sorta related.....what size breaker do you guys use with the VF2, I just purchased a 2002 model and it will be here next week, just trying to get the line ready so I can power it up right away. It has the 20HP motor on it. I think I read the amp draw was 40 max or something.........

    Thanks,
    Jim
    JM Fab

  5. #5
    Join Date
    Jul 2005
    Posts
    12177
    Quote Originally Posted by JMFabrications View Post
    Quick question sorta related.....what size breaker do you guys use with the VF2, I just purchased a 2002 model and it will be here next week, just trying to get the line ready so I can power it up right away. It has the 20HP motor on it. I think I read the amp draw was 40 max or something.........

    Thanks,
    Jim
    JM Fab
    My electrican installed 50amp panel breakers for my VF2s and used 6 gauge wire.
    An open mind is a virtue...so long as all the common sense has not leaked out.

  6. #6
    Join Date
    Mar 2005
    Posts
    1498
    070625-1602 EST USA

    JMF:

    We use 40 A Sq-D QO breakers for our VF-3s and #6 wire. Never have tripped one from the machine operation. However, we do not run high spindle loads.

    Our total run from the main breaker box to the furthest machine is about 75 ft for the cable run. Our leg-to-leg voltage is usually about 246 V.

    .

Similar Threads

  1. Wiring question
    By TSJ in forum Servo Motors / Drives
    Replies: 4
    Last Post: 05-15-2007, 07:20 PM
  2. Transformer wiring question
    By Bimmerkc1 in forum CNC Machine Related Electronics
    Replies: 3
    Last Post: 01-13-2007, 02:41 PM
  3. Wiring Question
    By elogicca in forum CNC Machine Related Electronics
    Replies: 6
    Last Post: 12-27-2006, 03:22 AM
  4. Wiring Question
    By The Wizard in forum CNC Machine Related Electronics
    Replies: 17
    Last Post: 01-04-2005, 07:11 PM
  5. Wiring Question
    By tjstraz in forum CNC Machine Related Electronics
    Replies: 1
    Last Post: 07-30-2004, 04:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •