586,035 active members*
3,712 visitors online*
IndustryArena Forum > CNC Electronics > Spindles / VFD > Huanyang VFD - is it normal to have +24 from "FOR" pin against "DCM" pin?
Results 1 to 8 of 8
    Mar 2007
    18
    Hi All,
    I'm having major problems trying to get my new AXBB-E controller to run the spindle. My router was working fine with a chinese controller (the MK4-V from cdxhctech) but I need to use probing g-codes which that controller doesn't support, so I'm trying to upgrade the controller to the CNCDrive AXBB-E, and it's not going well. I read as much as I could find and thought I had it hooked up to work - the same as the authors conclusion in this thread https://www.cnczone.com/forums/spind...nyang-vfd.html
    But the spindle will only turn on to about 100rpm or so, and the controller analogue voltage won't go over 3.8v (I have removed the jumper to set it to 10V range), while the inverter is looking for 10V
    I started checking voltages everywhere and got a shock (not literally) when I found +24V on the controller forward output control pin - so I unplugged everything and checked the voltage on the Inverter - see pic below - surely that's not normal?
    I think that 24V on the inverter forward input has damaged my controller board, the controller output pin that I had originally connected to the inverter forward input to no longer works.
    Attachment 449730
    Thoughts anyone - is this normal, or perhaps I did something bad while rewiring for the new controller and now my inverter is busted - and maybe my controller too?
    thanks
    Kevin.
    15362
    Re: Huanyang VFD - is it normal to have +24 from "FOR" pin against "DCM" pin?
    Quote Originally Posted by n0f8r View Post
    Hi All,
    Attachment 449730
    thanks
    Kevin.
    How are you trying to control the On / Off that can be normal to have 24v to switch FOR and DCM, 24v is an industry standard for these type of controls
    You have to get the PWM analog 0-10v working from your control before connecting it to the VFD Drive
    If you have only got 100RPM then your Parameter's in the VFD Drive have not been set correct
    Mactec54
    Mar 2007
    18
    @Matec54 But the forward pin is an input - so to my mind it should not have 24v on it with nothing plugged in -
    Pretty sure the VFD parameters are correct. As I mentioned - it was already working on the other controller - also as I mentioned - the new controller analogue output is not going beyond 3.8V so that's more likely the issue on the low RPM front.
    What I'm trying to understand - and perhaps look at the image and read my issue description again - nothing is plugged into the VFD input pins, only the power under the control pins is plugged in - and in that state - with nothing connected, the FOR pin is reading 24V.
    What that suggests to me, together with the fact that the first output pin on the new controller I had connected to FOR is no longer working - is that somehow I have broken my inverter, and it's also damaging my new controller when I hook it up.
    But I don't know - which is why I'm here....
    Dec 2003
    24221
    The PLC (I/O) on the Huanyang is typical of most VFD's where the input is a 'Sinking input' which means the PLC 'Sources' the 24v.
    What you are reading when testing with nothing connected, is the 24v appearing on the output pin through the opto-isolator input.
    To input the signal you take this 24v source through the opto down to DCM (common).
    This makes the (internal) opto conduct.
    The JPG shows an interface when using a G540 instead of a relay contact, also the 24vdc is supplied internally.
    Al.
    Albert E.
    Mar 2007
    18
    @Al_The_Man, thanks - that's very helpful. I'm getting closer to understanding now - so the controller output that's hooked up to FOR is supposed to pull to ground when active - and float when off?
    So hopefully all I need to do is figure out why my AXBB is not putting out 10V - and if I can't figure that out maybe I can just reprogram the VFD for 5V analog input - since with some more fiddling in Mach3 I can now read up to 4.8v on that pin. And the mystery of the one broken output can remain a mystery...
    Dec 2003
    24221
    @Al_The_Man, thanks - so the controller output that's hooked up to FOR is supposed to pull to ground when active - and float when off?
    Correct.
    Al.
    Albert E.
    15362
    If you are running a highspeed spindle then there is a minimum Parameter setting that needs to be set to protect the spindle if this is set correct then it will not be able to run at 100 RPM
    Al has already answered why you see the 24v, you just have to see if your control can switch it correctly, this is not a safe way to control an On / Off of a VFD Drive but a lot do it this way because of convenience instead of adding a Relay
    Mactec54
    15362
    Yes you can use the 0-5v control in your VFD to control the speed inMach3 you want the PWM set to 100
    Mactec54
  1. Multi-head or multiple extruder simotanious "follow me" copy print "mirror mode"
    By routermaker in forum 3D Printer / 3D Scanner Discussion
    Last Post: 10-26-2019, 02:34 AM
  2. How can do ""manual stepper motor sizing for "rack and pinion"calculation""???
    By Medhat93 in forum Mechanical Calculations/Engineering Design
    Last Post: 03-03-2018, 01:50 AM
  3. Replies: 5
    Last Post: 01-12-2014, 07:07 PM
  4. X Axis "Goes Off Pattern", "Awry", "Skewed", "Travels"
    By DaDaDaddio in forum Laser Engraving / Cutting Machine General Topics
    Last Post: 05-06-2013, 09:59 AM