    VFD Wiring from 220v Converter

    Hello friends,

    I am in the process of hooking up my 220v 1.5kw spindle and the plug that was attached to the VFD came off and before I fry the unit I wanted to ask here about the R S T hook ups. The unit came wired and used only two wires off the power cable although the cable actually has three. The power cable is coming from a Shen 220V 3000W from 110V power converter switch. I have downloaded a few manuals for this particular VFD but I have some conflicting information. Some say connect R and T, others say R and S and ground T.

    Please help!
    Attached Thumbnails Attached Thumbnails IMG_0505.jpg   IMG_0506.jpg  

  2. #2
    Join Date
    Dec 2003
    Posts
    24221
    Normally you NEVER connect a R,S or T to ground.
    The ground should be used as its name says and connect to the ground terminal, If you have 3 phase available from a convertor or? the RST go to the three terminal, it sounds like they used it previously on 1 phase, in that case R & S would normally work.
    If it is a simple 3 phase full wave rectifier on the input then any combination of the 1 ph in would work.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Aug 2010
    Posts
    55
    In examining the screw terminals I found broken wire fragments on both the S and T terminals. R appeared to be clean. Does wiring up only the S and T terminals sound right with nothing at P+?

  4. #4
    Join Date
    Dec 2003
    Posts
    24221
    I suspect P+ and PR are external braking? leave these unconnected to try.
    As I previously mentioned, if the input is as usual a 3 phase rectifier then it should not matter, if S & T appear to have been previously used, then I would try these, it is very rare to damage anything by picking the wrong RST pair, as these would be connected to 3 phase power anyway!.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5
    Join Date
    Aug 2010
    Posts
    55
    Thanks for the quick replies. I'm going to try the S and T. Is it true that if I want MACH3 to control this I need to get a bob board?? And for an estop any info on that? I did not receive a manual with this and I am unsure if the ones I downloaded are for this particular VFD

    Thanks again!

  6. #6
    Join Date
    Dec 2003
    Posts
    24221
    You will need a BOB that will convert the pwm to analogue for the VFD.
    Also outputs to VFD inputs for the M3/M4, fwd/rev.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Similar Threads

  1. Wiring 220V and 110V inside of CNC Electronics Cabinet
    By MRM RCModels in forum CNC Machine Related Electronics
    Replies: 14
    Last Post: 01-16-2010, 01:00 AM
  2. Wiring a 220v DOERR/Emerson Compressor Motor
    By Thazul in forum CNC Machine Related Electronics
    Replies: 5
    Last Post: 01-14-2010, 09:29 PM
  3. 220V europe to 120V US wiring
    By willy1067 in forum Laser Engraving / Cutting Machine General Topics
    Replies: 35
    Last Post: 02-25-2009, 04:05 AM
  4. 3 Phase Converter Wiring
    By ideffects in forum Phase Converters
    Replies: 7
    Last Post: 05-10-2008, 12:59 AM
  5. Phase Converter Wiring
    By freak_brain in forum CNC Machine Related Electronics
    Replies: 2
    Last Post: 03-15-2005, 07:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •