586,111 active members*
3,097 visitors online*
Register for free
Login
IndustryArena Forum > CNC Electronics > Spindles / VFD > Huanyang Chinese VFD settings and manual here!
Page 23 of 41 13212223242533
Results 441 to 460 of 808
  1. #441
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by davels View Post
    Hello mactec54, I come back to you with my spindle problem. The seller send me a new VFD and everything is running nice now. I still have to connect the ground on the spindle throw the screw like you send the picture. Thanks a lot for your help!
    I also buy a shielded cable, I should receive it next week. Does the shield has to be connected to the ground on VFD and Spindle?

    Thx, David
    Yes you need to connect the shield at both ends
    Mactec54

  2. #442
    Join Date
    Apr 2015
    Posts
    113

    Re: Huanyang Chinese VFD settings and manual here!

    Mind sharing your torque curve settings then?


    Doesnt shielding both ends make a ground loop, as well as most spindles not even having the 4th pin attached to the casing. I was always told, and have used with success just shielding the drain wire on the VFD end.
    Luthier/Woodworker/Machinist in NS, Canada.

  3. #443
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by jahnj0584 View Post
    Mind sharing your torque curve settings then?


    Doesnt shielding both ends make a ground loop, as well as most spindles not even having the 4th pin attached to the casing. I was always told, and have used with success just shielding the drain wire on the VFD end.
    No it can't cause a Ground loop, if everything is bonded to Ground

    Cable Shields Terminated at one end, only provide electrostatic protection, against low frequency, capacitive coupled interference and emission, read first snip below

    If the ( Source and the receiver ) ( the source being the VFD and the receiver being the Spindle ), are both connected to Ground, then the Shields must be connected at both ends

    As far as a Torque curve is I have provided this in other posts, I do not post this as if done incorrectly and to aggressive, you will smoke your spindle motor in seconds, of starting it, most should be using what is the VFD default for these Spindles

    Can you make them better, very slightly, these spindles have max torque at near max RPM so you have very little to play with, anything below the max RPM

    Some good snips below, I have posted, will give users how shield need to be terminated to be effective, if you need more ways for shields to be terminated I can post more examples
    Attached Thumbnails Attached Thumbnails Grounding Shields-2.PNG   Grounding Shields-3.PNG   Grounding Shields-5.PNG  
    Mactec54

  4. #444
    Join Date
    Mar 2014
    Posts
    1131

    Re: Huanyang Chinese VFD settings and manual here!

    Hi again,

    This time I'm trying to do the wiring from cnc4pc M16 to Huanyang vfd.

    I've connected 12v external power to the board but I don't know which pin on M16 should I connect where on the VFD. The spindle will be only running in one direction (fwd) and will be running with analog 0-10v signal.

    Any help would be appreciated.
    Best,
    Suat
    Attached Thumbnails Attached Thumbnails M16_VFD.jpg  

  5. #445
    Join Date
    Mar 2014
    Posts
    1131

    Re: Huanyang Chinese VFD settings and manual here!

    I figured some of the pins but some are still unknown.
    Attached Thumbnails Attached Thumbnails M16_Huanyang_wiring.jpg  

  6. #446
    Join Date
    Apr 2015
    Posts
    113

    Re: Huanyang Chinese VFD settings and manual here!

    You only need 3.

    Its different if you are doing the RS+ route
    Attached Thumbnails Attached Thumbnails ss (2017-12-20 at 07.08.37).jpg  
    Luthier/Woodworker/Machinist in NS, Canada.

  7. #447
    Join Date
    Oct 2012
    Posts
    2

    Re: Huanyang Chinese VFD settings and manual here!

    good morning
    How can I change direction 1.5kw spindle rotation from inverter
    huanyang model HY01D523B
    thank you in advance (I write from Italy)

  8. #448
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by birillo406 View Post
    good morning
    How can I change direction 1.5kw spindle rotation from inverter
    huanyang model HY01D523B
    thank you in advance (I write from Italy)
    Check your spindle wiring U=Pin 1 V=Pin 2 W=Pin 3, if this is correct then change, any 2 wires
    Mactec54

  9. #449
    Join Date
    Oct 2012
    Posts
    2

    Re: Huanyang Chinese VFD settings and manual here!

    thank mactec54 for the answer, I have run and it's all OK!
    I wanted to ask if it is possible to connect "emergency mushroom" to the aforementioned vfd and possibly how
    Thank you in advance
    translated with Google

  10. #450
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by birillo406 View Post
    thank mactec54 for the answer, I have run and it's all OK!
    I wanted to ask if it is possible to connect "emergency mushroom" to the aforementioned vfd and possibly how
    Thank you in advance
    translated with Google
    Yes there are more than one way to do this, the most used is with the VFD Drives Relays, you will have to test with your meter which Relay closes when you start the VFD

    PD052 Multi-Output 3(FA, FB, FC function) Factory Setting:02 Set this Parameter to what your manual requires for this to work

    I think the FC connection is the correct one, for your Estop circuit, not sure though

    Fault Indication: The contact will act when the inverter detects abnormal conditions.
    Mactec54

  11. #451
    Join Date
    May 2011
    Posts
    1

    Re: Huanyang Chinese VFD settings and manual here!

    HI all,

    Please help,
    4kw motor, 220v single phase in, 220v three phase out, Haunyang 4kw inverter.

    Set all the parameters as suggested by mactec54 in earlier posts, obviously changing the frequencies to 50 Hz, and the machine works wonderfully in manual operation, however the problem starts when I need to use a 0-5v input from the control system, changed PD 001 and 002 to setting 1 and PD 070 to setting 1 for 0-5v input, moved the jumper J1 to VI and have my variable 0-5v hooked into VI and ACM.

    just doesn't seem to work and need help and guidance please

  12. #452
    ericks Guest

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by KeithJ View Post
    HI all,

    Please help,
    4kw motor, 220v single phase in, 220v three phase out, Haunyang 4kw inverter.

    Set all the parameters as suggested by mactec54 in earlier posts, obviously changing the frequencies to 50 Hz, and the machine works wonderfully in manual operation, however the problem starts when I need to use a 0-5v input from the control system, changed PD 001 and 002 to setting 1 and PD 070 to setting 1 for 0-5v input, moved the jumper J1 to VI and have my variable 0-5v hooked into VI and ACM.

    just doesn't seem to work and need help and guidance please
    Are you having problems with starting the drive or speeding it up and down?

  13. #453
    Join Date
    Apr 2015
    Posts
    113

    Re: Huanyang Chinese VFD settings and manual here!

    Acm and dcm must be daisy chained so they both go to ground. I so had this issue.
    Luthier/Woodworker/Machinist in NS, Canada.

  14. #454
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by KeithJ View Post
    HI all,

    Please help,
    4kw motor, 220v single phase in, 220v three phase out, Haunyang 4kw inverter.

    Set all the parameters as suggested by mactec54 in earlier posts, obviously changing the frequencies to 50 Hz, and the machine works wonderfully in manual operation, however the problem starts when I need to use a 0-5v input from the control system, changed PD 001 and 002 to setting 1 and PD 070 to setting 1 for 0-5v input, moved the jumper J1 to VI and have my variable 0-5v hooked into VI and ACM.

    just doesn't seem to work and need help and guidance please
    Do you have a relay to switch between FWD and DCM

    The 0-5v is only to change the speed the FWD is for the On / Off control, you can use a jumper connecting FWD and DCM just to try it
    Mactec54

  15. #455
    Join Date
    Mar 2014
    Posts
    1131

    Re: Huanyang Chinese VFD settings and manual here!

    Can you run an RC type brushless motor with a Huanyang VFD? I have a 4kw VFD and a 3kw 24v brushless inrunner motor. It would be nice if I can use them together.

  16. #456
    Join Date
    Dec 2017
    Posts
    77

    Re: Huanyang Chinese VFD settings and manual here!

    For that, you need a 24 V variable DC power supply, not a VFD. At 125 amps max output, it'll be pricey!

    Also, I think that type of motor has a limited RPM range.

  17. #457
    Join Date
    Feb 2018
    Posts
    0

    Re: Huanyang Chinese VFD settings and manual here!

    Hey guys, I'm new here. I have a 2.2kw spindle and single phase VFD. I have a basic Breakout board in my controller. Without having to read 38 pages of multiple spindle set ups, does anybody know the correct signal wiring from the controller to the VFD and what settings I need? I want to control on/off and speed from Mach 3.

  18. #458
    Join Date
    Feb 2018
    Posts
    0

    Re: Huanyang Chinese VFD settings and manual here!

    Here is the board and vfd I’m using.



    Oh yeah here is my table. Trying to get it cutting today!!
    Attached Thumbnails Attached Thumbnails AAD940BB-7138-4CF0-B9BD-C6900F36FDD4.jpg  

  19. #459
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Hyperryd View Post
    Here is the board and vfd I’m using.



    Oh yeah here is my table. Trying to get it cutting today!!
    For the On /Off you connect the FOR and DCM to the Breakout Board where it says Spindle Switch

    For the Speed control you Use VI and ACM to the Breakout Board Where it says Speed Control this is your 0-10v PWM

    You need to add a 12v Dc power supply to the Breakout Board where it says 12v-24v Power

    Your 240v Ac single phase input Power wiring is best connected to R and T terminals and Ground to the Ground Terminal

    You need to use Shielded Cable for the VFD to Spindle Connection, and need to make sure the 4th Pin is connected inside the spindle

    These Parameters need to be set, if you have not already set them

    Huanyang Mactec54

    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock

    PD001=0 (1 For Remote Control)

    PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )
    ( J1 Also Needs to be set for Terminal Control )

    PD003=400

    PD004=400

    PD005=400

    PD007=20

    PD008=220 (Motor Rated Voltage, If you have 120v spindle then set to 120v )

    PD009=15

    PD010=8

    PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014 Acceleration=10 ( Adjust to suit)

    PD015 Deceleration=10 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD023=0

    PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )

    PD142=9 ( Motor Max Amps 2.2Kw Spindle 9 amp )

    PD143=2 ( Motor Number of Poles)

    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    PD041=8 ( Carrier Frequency up to 10 Max for these Spindle motors)

    PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )

    PD72=400

    PD73=120 ( 100 Minimum Setting )
    Mactec54

  20. #460
    Join Date
    Feb 2018
    Posts
    0

    Re: Huanyang Chinese VFD settings and manual here!

    I have 24v supplied to the 12-24v terminals. Should I lower to 12v? I had this table built from a guy who didn’t send any diagrams. Not happy about that but I am learning fast. I appreciate your help.

    This is is the inside of the controller.

Page 23 of 41 13212223242533

Similar Threads

  1. Car hoist 3phase settings on huanyang vfd
    By pietskiet in forum Spindles / VFD
    Replies: 1
    Last Post: 10-21-2019, 10:04 AM
  2. Replies: 4
    Last Post: 02-16-2017, 05:42 AM
  3. Huanyang SL-240EE Manual (SL Series Manual for Vector VFD)
    By Cogolith in forum Phase Converters
    Replies: 2
    Last Post: 05-24-2016, 04:19 AM
  4. Huanyang inverter PD settings
    By jamriggsy in forum Phase Converters
    Replies: 2
    Last Post: 03-15-2013, 04:54 PM
  5. Huanyang 2.2kw VFD, 0-10v 3600rpm settings?
    By EmeraldIsleforg in forum Phase Converters
    Replies: 1
    Last Post: 09-23-2012, 03:00 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •