    Re: Huanyang Chinese VFD settings and manual here!

    keiner99

    You need a relay to switch the DCM and Forward top row of the VFD above where you have the 0-10v, you need to set PD044=01

    so an output from Mach 3 that turns the Relay on for M3 and off for M5

    Fix your Ground wire connection, these are important, also check the pin 4 at the spindle for Ground, continuity between Pin 4 and the spindle body, this is very important, most have to be modified

    This is how you would do it without the reverse
    Mactec54

  2. #142
    Join Date
    Jun 2016
    Posts
    9

    Re: Huanyang Chinese VFD settings and manual here!

    Hello!
    I'm not sure if i have understand you right. Attached you will find a picture - am I right?
    Attached Thumbnails Attached Thumbnails IMG_5204.jpg  

  3. #143
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by keiner99 View Post
    Hello!
    I'm not sure if i have understand you right. Attached you will find a picture - am I right?
    Yes that is correct, but check the DCM on the top Terminal row is the same as the bottom row DCM, it should be, what you can do to check is to just use a jumper wire, between the FOR and the DCM this should start your spindle if all your settings are correct, you can not run it like this, only test

    If it does not start with this, then there may be a jumper that you need to change Do the PD044 setting try this first, is the 0-10v output working, have you checked it's output to see if the voltage changes as you change the speed in Mach3
    Mactec54

  4. #144
    Join Date
    Jun 2016
    Posts
    9

    Re: Huanyang Chinese VFD settings and manual here!

    Hello!
    I have connected the VFD like on the attachment.

    The 0-10V output from my breakout board is working. PD001=1, PD044=01. When I start the VFD is run up to 24000 rpm, even it get 3V from the 0-10V cable. What is wrong?

    EDIT: I have tested both DCM ports - the problem is the same

    Franz

  5. #145
    Join Date
    Jul 2014
    Posts
    10

    Re: Huanyang Chinese VFD settings and manual here!

    xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx

  6. #146
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by keiner99 View Post
    Hello!
    I have connected the VFD like on the attachment.

    The 0-10V output from my breakout board is working. PD001=1, PD044=01. When I start the VFD is run up to 24000 rpm, even it get 3V from the 0-10V cable. What is wrong?

    EDIT: I have tested both DCM ports - the problem is the same

    Franz
    You can't just try each DCM ports you have to check with a meter with the power off, this is very unusual that there are ( 2 ) DCM ports, and I suspect, it is either labeled wrong or that you may have a VFD that is a copy, a poor copy of the real thing

    looking from the front,to the right side of the terminal block you will see J1 this is a jumper that may need changing, move the jumper to VI

    It will look similar to this photo
    Attached Thumbnails Attached Thumbnails J1 Jumper.PNG  
    Mactec54

  7. #147
    Join Date
    Jun 2016
    Posts
    9

    Re: Huanyang Chinese VFD settings and manual here!

    Hello!
    I have already made an circuit continuity test and it has continuity. so I think the DCM ports are the same... the J1 jumper was already on VI... any other suggestions?

    Franz

  8. #148
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by keiner99 View Post
    Hello!
    I have already made an circuit continuity test and it has continuity. so I think the DCM ports are the same... the J1 jumper was already on VI... any other suggestions?

    Franz
    That is correct if they have continuity either could be used, strange the jumper was already set, as this disables the keyboard when set on V1, this may be backwards, but try the PD044 change first
    Try PD044=02
    Mactec54

  9. #149
    Join Date
    Jun 2016
    Posts
    9

    Re: Huanyang Chinese VFD settings and manual here!

    PD044=02 --> same problem

  10. #150
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by keiner99 View Post
    PD044=02 --> same problem
    Are these 2 connections correct VI has the 0-10v and the common to ACM are correct, with these ( 2 ) wires disconnected, connect them to you meter does the voltage change when you change the speed command from Mach3
    Mactec54

  11. #151
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    keiner99

    I see you did not set these Parameters in your Parameter list, you need these set

    PD70=0 ( This may need to be set to 1 for normal use )
    PD72=400
    PD73=120
    Mactec54

  12. #152
    Join Date
    Jun 2016
    Posts
    9

    Re: Huanyang Chinese VFD settings and manual here!

    Hello!
    Now I have also set PD44=1, PD70=0, PD72=400 and PD73=120. Same problem.

    The 0-10V signal was on VI and ground on ACM. I have made two pictures with 10000rpm and 20000rpm ( set on mach3).There you can see, that the voltage changes (Y)
    Attached Thumbnails Attached Thumbnails IMG_5224.jpg   IMG_5226.jpg  

  13. #153
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by keiner99 View Post
    Hello!
    Now I have also set PD44=1, PD70=0, PD72=400 and PD73=120. Same problem.

    The 0-10V signal was on VI and ground on ACM. I have made two pictures with 10000rpm and 20000rpm ( set on mach3).There you can see, that the voltage changes (Y)
    That all looks good

    Try this Parameter PD002=1
    Mactec54

  14. #154
    Join Date
    Jun 2016
    Posts
    9

    Re: Huanyang Chinese VFD settings and manual here!

    you are a hero - it works

    but i have another small problem: When I say 24000rpm in mach 3 i get 23900rpm on the inverter, but when I reduce the rpm in mach3 the difference get bigger and bigger:

    on mach3 | on the inverter

    24000rpm - 23910rpm
    20000rpm- 20470rpm
    16000rpm- 17220rpm
    12000rpm-14340rpm
    10000rpm-12960rpm
    8000rpm-11700rpm

    Where can i calibrate it?

  15. #155
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by keiner99 View Post
    you are a hero - it works

    but i have another small problem: When I say 24000rpm in mach 3 i get 23900rpm on the inverter, but when I reduce the rpm in mach3 the difference get bigger and bigger:

    on mach3 | on the inverter

    24000rpm - 23910rpm
    20000rpm- 20470rpm
    16000rpm- 17220rpm
    12000rpm-14340rpm
    10000rpm-12960rpm
    8000rpm-11700rpm

    Where can i calibrate it?
    So did you have PD044 set to 01 or 02, or do both work

    Calibrate, this can be hit and miss with Mach3 under motor tuning you can play with the spindle settings,
    Under Config you have Pulley selection

    Under Ports & Pins you have spindle setup motor control

    Some PWM controls also have a Trimpot to adjust the Voltage

    So lots to play with, but will mostly be to do in the spindle setup adjusting the Frequency, if the other pulley settings Etc are correct
    Mactec54

  16. #156
    Join Date
    Jun 2016
    Posts
    9

    Re: Huanyang Chinese VFD settings and manual here!

    ok thank you very much

    PD44 01 or 02 work both... which would you take?

  17. #157
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by keiner99 View Post
    ok thank you very much

    PD44 01 or 02 work both... which would you take?
    02 is the Drive default,so that is why I don't have it in my Parameter list, it's just one parameter that normally is not needed to be changed

    There is another Parameter that can affect the speed so if all else fails you can play with this parameter

    PD071 default it is set at 20 it has a range of 0-50 with can change how the speed is controlled, only go there after the mach 3 settings have been setup
    Mactec54

  18. #158
    Join Date
    Jun 2015
    Posts
    10

    Re: Huanyang Chinese VFD settings and manual here!

    Hi all,
    I have bought myself the Routakit SDX machine everything is built I am just stuck on the Huanyang VFD. I also have the 1.5 spindle
    the parameters that I have set for the VFD are as follows.
    PD013 - 8
    PD001 - 0
    PD002 - 1
    PD004 - 400
    PD005 - 400
    PD006 - 2.5
    PD007 - 0.5
    PD008 - 220
    PD009 - 15
    PD010 - 8
    PD011 - 120
    PD014 - 5
    PD015 - 5
    PD023 - 0
    PD025 - 1
    PD041 - 8
    PD072 - 400
    PD073 - 120
    PD141 - 220
    PD142 - 7
    PD143 - 2
    PD144 - 3000

    and in that order if that matters :?: I have seen some people believe the order you do matters but others say different.

    The spindle runs BONUS!! no overheating . but I have come across one issue. I have the control knob on the VFD. start spindle on slow with the knob turned left as I turn the knob fully right to achieve maximum RPM(24000) it stays on 15600ish. does anyone know why this is??

    Thanks in advance
    ACE8421

  19. #159
    Join Date
    Jan 2005
    Posts
    15362

    Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Ace8421 View Post
    Hi all,
    I have bought myself the Routakit SDX machine everything is built I am just stuck on the Huanyang VFD. I also have the 1.5 spindle
    the parameters that I have set for the VFD are as follows.
    PD013 - 8
    PD001 - 0
    PD002 - 1
    PD004 - 400
    PD005 - 400
    PD006 - 2.5
    PD007 - 0.5
    PD008 - 220
    PD009 - 15
    PD010 - 8
    PD011 - 120
    PD014 - 5
    PD015 - 5
    PD023 - 0
    PD025 - 1
    PD041 - 8
    PD072 - 400
    PD073 - 120
    PD141 - 220
    PD142 - 7
    PD143 - 2
    PD144 - 3000

    and in that order if that matters :?: I have seen some people believe the order you do matters but others say different.

    The spindle runs BONUS!! no overheating . but I have come across one issue. I have the control knob on the VFD. start spindle on slow with the knob turned left as I turn the knob fully right to achieve maximum RPM(24000) it stays on 15600ish. does anyone know why this is??

    Thanks in advance
    ACE8421
    It does not matter what order or how you set the Parameters, as long as they do get set correctly

    You are missing a critical Parameter, and will damage your spindle, I'm not sure why people can't follow the parameters I post, the list I did has been around everywhere for the last 5 years

    PD003=400 this must be set this is one of the critical Parameters and you don't have it in your list, a guess you have left it at the Default of 0/50hz, if this Parameter is left at the 0/50Hz it will damage your Spindle

    PD002=0 this needs to be Zero if using the keyboard control, only if you use remote control you change it to ( 1 )

    You have added 2 other Parameters which should be left as Default

    PD023=0
    PD025=0

    If they are not in list of Parameters to change then you should not mess with any other parameters, unless you are an expert VFD control programer
    Mactec54

  20. #160
    Join Date
    Jun 2015
    Posts
    10

    Re: Huanyang Chinese VFD settings and manual here!

    Hi mactec54

    I have got the variable speed control on the VFD so I have left the PD002 as is but the others I have changed and still having no luck. turn the knob fully right and it still only reaches 15600 RPM??
    Would I just be better of resetting the VFD with PD013 -8 and going through it all again?

    kind regards
    Ace8421

Page 8 of 41 67891018

Similar Threads

  1. Replies: 6
    Last Post: 05-04-2024, 04:05 PM
  2. Car hoist 3phase settings on huanyang vfd
    By pietskiet in forum Spindles / VFD
    Replies: 1
    Last Post: 10-21-2019, 10:04 AM
  3. Huanyang SL-240EE Manual (SL Series Manual for Vector VFD)
    By Cogolith in forum Phase Converters
    Replies: 2
    Last Post: 05-24-2016, 04:19 AM
  4. Huanyang inverter PD settings
    By jamriggsy in forum Phase Converters
    Replies: 2
    Last Post: 03-15-2013, 04:54 PM
  5. Huanyang 2.2kw VFD, 0-10v 3600rpm settings?
    By EmeraldIsleforg in forum Phase Converters
    Replies: 1
    Last Post: 09-23-2012, 03:00 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •