    Aluminum wire for connecting machines

    Any reason to not use aluminum wire for the incoming line to the machine? Correctly installed with the goop the electricians put on the connection of course.

    I am moving 26 machines to a new location and the cost saving using aluminum instead of copper for the new wiring is a reasonable sum of money.
    An open mind is a virtue...so long as all the common sense has not leaked out.

  2. #2
    Join Date
    Oct 2005
    Posts
    21
    Use of the goop keeps the aluminum wiring from oxidizing and creating a high resistance connection. The problem with using aluminum wire for equipment with a high current draw is that it still gets warm, expands, deforms slightly due to its' plasticity at elevated temperature, then keeps that shape when it cools. It is now ever so slightly looser a connection than before. Over time, the connection gets looser and looser and eventually becomes a high resistance connection, and a fire hazard. If you must use aluminum wire to connect your machines, protect yourself by re-tightening all connections on a regular basis, and get someone in to do an IR scan of your connections to make sure none of them are running at a higher temperature than they should, because a connection running at an elevated temperature won't be visible until it starts to burn the insulation off the wire.

  3. #3
    Join Date
    Apr 2005
    Posts
    713
    My VF-2ss is hooked up with aluminum wire and has been just fine since '07. I don't use mine as much as you use your machines, but the connections have never loosened up at all. I check them roughly once every 6 months.

  4. #4
    Join Date
    Jan 2007
    Posts
    1389
    alum will work fine for a smaller haas they run 5 ton a/c units all the time in AZ on them and they run on and off for ever.
    we had 2 hardinge ahc'c and a omniturn running in our garage with alum wire back in 92 ( not because it was cheap but thats teh way the garage was wired)they ran bar feed work and anyone that knows hardinge ahcs know they draw tons of power. so I would say you would be fine. and the goop is needed.
    only thing with alum is get into the habit of check tighness alot during the 1st 3 months then every 6months- a year after that.

  5. #5
    Join Date
    Jun 2007
    Posts
    67
    The savings will be great but will it be to code?
    What about your insurance?

  6. #6
    Join Date
    Jul 2005
    Posts
    12177
    ....protect yourself by re-tightening all connections on a regular basis,...

    ...I check them roughly once every 6 months...

    ...check tighness alot during the 1st 3 months then every 6months- a year after that...

    Everybody seems to be singing the same tune; which is a deal killer.

    When I do the calculation to amortize the initial saving over the nuisance value of having to get into the back of the machines on a regular basis over the years it is not worth it.
    An open mind is a virtue...so long as all the common sense has not leaked out.

  7. #7
    Join Date
    Mar 2010
    Posts
    1852
    You might look at the copper as an investment! It will probably be worth much more in the future.
    Two Haas VF-2's, Haas HA5C, Haas HRT-9, Hardinge CHNC 1, Bother HS-300 Wire EDM, BobCAD V23, BobCAD V28

  8. #8
    Join Date
    Jan 2005
    Posts
    15362
    Geof

    Could you not take most/some of the wire from your old shop & reuse it were you can
    Mactec54

  9. #9
    Join Date
    Jul 2005
    Posts
    12177
    Quote Originally Posted by mactec54 View Post
    Geof

    Could you not take most/some of the wire from your old shop & reuse it were you can
    We will but not much will be useful. In the old shop the transformer and distribution panel were about in the middle of the machines. In the new shop they are on a wall at one end so most of the wire runs are a lot longer. The transformer is also mounted high up so we get back all the floor space that used to be lost to the clearance code requires in front of the panel. It is a case of gain some lose some; we gain floor space at the cost of new wiring.
    An open mind is a virtue...so long as all the common sense has not leaked out.

  10. #10
    Join Date
    Jan 2007
    Posts
    1389
    Geof
    My experance with the alum wire is in a/c on residential and in 120 degree heat that goes down to 30 degrees in the winter time. in a shop it may not work the same as a wont fluctuate 70º
    the only place I had to check/tighten the wire is 90% at the main fuse box thats outside on the east and west walls.

    hope that helps
    Delw

  11. #11
    Join Date
    Dec 2003
    Posts
    24221
    I am not a particular lover of aluminum wiring, you are supposed to clean any trace of (invisible) oxide off before applying the inhibitor, also you should only be using aluminum or aluminum/copper compatible connection points.
    If yours are copper only rated, you may have problems.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  12. #12
    Join Date
    Jul 2005
    Posts
    12177
    Quote Originally Posted by Al_The_Man View Post
    ....If yours are copper only rated, you may have problems.
    Al.
    I won't have problems, I am going to be conservative and go with copper. The cost difference is only four 'latte factors'. A latte factor is my annual expense at Starbucks buying lattes, steamed milks, chai teas, what-have-you for me and others.
    An open mind is a virtue...so long as all the common sense has not leaked out.

  13. #13
    Join Date
    Mar 2010
    Posts
    1852
    Quote Originally Posted by Geof View Post
    I won't have problems, I am going to be conservative and go with copper. The cost difference is only four 'latte factors'. A latte factor is my annual expense at Starbucks buying lattes, steamed milks, chai teas, what-have-you for me and others.
    I really think that is a good decision Geof. Many factors make it a better choice.

    Mike
    Two Haas VF-2's, Haas HA5C, Haas HRT-9, Hardinge CHNC 1, Bother HS-300 Wire EDM, BobCAD V23, BobCAD V28

  14. #14
    Join Date
    Feb 2010
    Posts
    1184
    Quote Originally Posted by Machineit View Post
    I really think that is a good decision Geof. Many factors make it a better choice.

    Mike
    I agree 100% Although there may be many testimonials in favor of aluminum wiring, I think you will sleep better knowing you went with the copper.

    Congrats on the new shop also.

  15. #15
    Join Date
    Apr 2005
    Posts
    713
    Quote Originally Posted by haastec View Post
    I agree 100% Although there may be many testimonials in favor of aluminum wiring, I think you will sleep better knowing you went with the copper.
    Even though I'm running aluminum to my mill and have not had any problems, I agree with the above. If I had a choice at the time, I would've went with copper as well.

    So Geof, when do we get to see pictures of the new digs?

  16. #16
    Join Date
    Jul 2005
    Posts
    12177
    Quote Originally Posted by Matt@RFR View Post
    Even though I'm running aluminum to my mill and have not had any problems, I agree with the above. If I had a choice at the time, I would've went with copper as well.

    So Geof, when do we get to see pictures of the new digs?
    Here are three; one looking from the end of the shop toward the upstairs offices, one on the lower level looking down the shop and one looking from the upstairs offices.

    I am going to start a thread showing the move-in over the next few weeks. At least it is not a long trip, less than 100yards across the parking lot separating this building from the one we have leased for 18 years. No more lease payments after the end of this year.
    Attached Thumbnails Attached Thumbnails DownFaceOffice.jpg   DownFaceEnd.jpg   FromOffice.jpg  
    An open mind is a virtue...so long as all the common sense has not leaked out.

  17. #17
    Join Date
    Feb 2010
    Posts
    1184
    Nice space Geof. Just watch that first step leaving the upstairs office!

  18. #18
    Join Date
    Jul 2005
    Posts
    12177
    Quote Originally Posted by haastec View Post
    Nice space Geof. Just watch that first step leaving the upstairs office!
    Yes that way out is a big step. You probably guessed those doors are for moving desks, etc into the offices by forklift rather than carrying them up the stairs
    An open mind is a virtue...so long as all the common sense has not leaked out.

  19. #19
    Join Date
    Jan 2007
    Posts
    1389
    Can I apply for a job? or you can adopt me
    Nice place Geof your hard work looks like its paying off, Congrats.

    Delw

  20. #20
    Join Date
    Apr 2006
    Posts
    235
    What kind of surface is it? Tiled? Coated? Just curious. . .

Page 1 of 2 12

Similar Threads

  1. Connecting Bridgeport CNC machines to Windows 2008 Active Directory OR work around
    By christineotto in forum Computers / Desktops / Networking
    Replies: 1
    Last Post: 04-29-2013, 03:12 AM
  2. Looking at switching from Mitts to Aggie wire machines
    By RPT in forum EDM Discussion General Topics
    Replies: 0
    Last Post: 12-21-2010, 04:05 PM
  3. Connecting bipolar motors without knowing which wire is which?
    By Witsenburg in forum Stepper Motors / Drives
    Replies: 1
    Last Post: 05-12-2007, 04:29 PM
  4. connecting to machines
    By watzmann in forum Community Club House
    Replies: 2
    Last Post: 06-20-2006, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •