    A different type of homing/limit switch

    So I am sitting here trying to figure out a new system because my current home/limit switches are way to susceptible to false readings due to moisture.

    Has anyone every used something like a dowel pin mounted into an acetal type block? The idea is to electrically isolate the dowel pin from the table, but when the table bumps into it, it would stop. The micro rocker switches are not very accurate.

    I am curious if such a system exists?

  2. #2
    Join Date
    Dec 2003
    Posts
    24221
    Well the principle has been around for eons, a microswitch in a sealed enclosure and is tripped with a plunger that traditionally has taken many forms, depending on the application?
    Why the electrical isolation? normally with MicroSwitch the contacts are not part of the operator?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Jun 2010
    Posts
    1414
    I guess the fluid that gets in there is what triggers a false reading and the table stops.

    If I had a tall rod, that the table will "bump" into when it touches it, it will send the ground pulse required to stop the machine properly.

  4. #4
    Join Date
    Aug 2009
    Posts
    986
    There's no reason that won't work. You're just replacing the microswitch with a much larger switch.

    It does sound bulky, and therefore is prone to being bent, tweaked, or otherwise knocked out of position by accident. If you want repeatable homing, this may not be the best method.

    Frederic

  5. #5
    Join Date
    Jun 2010
    Posts
    1414
    I am thinking like 1" thick, and under the table touching the carriage, or someplace that it won't interfere. It doesn't have to be a rod, it can be any piece of conductive metal (likely aluminum) that is electrically isolated from the rest of the table, that will ground out when the table bumps into it.

    In any case, I would love repeatable homing.

  6. #6
    Join Date
    Dec 2003
    Posts
    24221
    I use these hermetically sealed Microswitch.
    ebay 390370013513
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  7. #7
    Join Date
    Jan 2006
    Posts
    2985
    Nateman

    Your proposed design would not allow any overtravel which may be bad news if for some reason a wire became disconnected during homing. If you use the right switch, it should be quite repeatable.

    Matt

  8. #8
    Join Date
    Apr 2005
    Posts
    861
    The overtravel problem is a real one. You'll need to back it up with a preloaded spring assembly. Even during normal homing operation there will always be a delay (even if very small) between when the home switch fires and when the axis stops. A totally rigid assembly will be stressed unless you implement some compliance in it.
    You'll also need to ensure it stays dry. Any beads of moisture on either conducting surface will cause the switch to trigger early. Sounds like a decent idea but I am pretty sure it would be easier to install a sealed switch, as Al has done.
    LongRat
    www.fulloption.co.uk

  9. #9
    Join Date
    Jun 2010
    Posts
    1414
    Al's switches are $20 per axis. I have enough scrap to make the poles. I will get the switches for my larger machine, but one day when I get fed up with the false stops I will try to make a acetal stop.

    I already took measures to waterproof the current switches, but its hard to stop moisture.

  10. #10
    Join Date
    Aug 2006
    Posts
    1602
    What about magnetic proximity switches? They're totally sealed and non contact, but I suppose you might have some issues if you get magnetic swarf on them...

  11. #11
    Join Date
    Aug 2008
    Posts
    962
    Nateman,

    Are you certain the false trips are not due to noise?

    I had some issues with that when I first got my machine running & was seeing lots of unexpected stops.

    Don't know about your level of knowledge on the subject, but there were some wiring issues I didn't fully understand. Especially concerning the difference between a neutral & a ground.

    It's taken me a while to sort things out but now that I have my machine is running quite reliably.

Similar Threads

  1. Galil Limit switch Homing
    By Karl_T in forum Controller Cards
    Replies: 0
    Last Post: 03-04-2011, 11:38 PM
  2. Homing and limit switch
    By shadowless in forum Taig Mills / Lathes
    Replies: 14
    Last Post: 09-19-2009, 01:26 AM
  3. MICRO Adjustment of Lever Type Limit Switch
    By scratch_6057 in forum DIY CNC Router Table Machines
    Replies: 0
    Last Post: 05-16-2007, 02:47 PM
  4. what is the best homing and limit switch setup?
    By Bryscnc in forum Machines running Mach Software
    Replies: 1
    Last Post: 09-28-2006, 11:37 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •