When I power on machine, I get alarm
434 SERVO ALARM : Z AXIS DETECT ERR
...sometimes combined with
403 SERVO ALARM : (VRDY OFF)
And I can not start machine.
This used to happen in past, but I was able to loose this alarm by turning off an on machine, but now it can not be done.
Machine:
KIA KV25 VMC
Fanuc 0M-C
Z axis Servo motor:
A06B-0514-B105
AC - 5S / 3000
Z axis Servo amplifier:
A06B-6058-H025
S Series Drive (single axis)
Immediately after I switch on the main power on the machine,
red LED "LV" goes on.
After powering on of the CNC, I can see
DGN 0722#6=1 (0100 0000)
That should say "low voltage" ?
Input voltage (from external transformer) is OK - 3 x 245 V.
I checked some pins on amplifier board that are called B1, B2 and B3.
There is voltage only between B1 and B3. Is that OK?
What is procedure in this situation, that to check...
or just to get new amplifier?