I recently replaced APC batteres on fanuc series io - mate mill. and tried resseting the reference point parameter but i always get a "write protect" mesage.
need help on how to perform zero return (300 alarm)
thanks!
I recently replaced APC batteres on fanuc series io - mate mill. and tried resseting the reference point parameter but i always get a "write protect" mesage.
need help on how to perform zero return (300 alarm)
thanks!
What kind of machine do you have?
What value do you have in parameter 1815?
Regards
Alex
parameter 1815 has Apc set to 1 and APZ set to 0 when i try to change the zero to 1 it says "write protect"
The machine is an Ajax spark X with fanuc series io - mate.
Thanks!
Push the hard key offsets/settings, go in the setting menu by pushing the soft key settings. In MDI mode change PWE=0 to a 1.An alarm 100 will appear! (meaning pwe=1)
Try to change parm 1815 bit 4 to a one. Alm 000 will apear to power off the control. Change PWE=1 to a zero.
Power off and on the control. Make sure the zero position of the axis is the correct one.
Alex.