    Alarm 23 - excess error (speed)

    Mitsubishi Fr-sf-2-26K. Top board SF-CA. Option card SF-BS. The original problem was a dead power supply after running the night before. Replaced PS, then found shorted IGBT in base. Replaced IGBT. Started getting Alarm 23. We tried the top board (SF-CA) on another base; it worked. We had motor checked by motor shop and also megged it out. We put drive in open-loop; it still won't run. We tried another sensor/PLG card; no good. The only thing I know thing know that is left is the SF-BS card. I'm not sure what all this card does. We do not do orientation. I have not ohmed out cabling, but do not think this is the culprit. I may try the other top board out of the good unit but did not want to chance messing it up.

    Any thoughts? I hate to send this thing to Mits, but that may be next.....

  2. #2
    Join Date
    Jan 2011
    Posts
    350
    Next would be to test the encoder and the encoder cable to see if they're alright.

  3. #3
    Join Date
    May 2012
    Posts
    0
    Quote Originally Posted by botha.y View Post
    Next would be to test the encoder and the encoder cable to see if they're alright.
    It's an older spindle motor and probably doesn't have an encoder, just a PLG. PLGs cause a lot of weird problems, including blowing transistors. That's what I suspected at first. You need a scope to adjust them.

    But he said it won't run in open loop, which bypasses the PLG. That being the case, I'd look hard at the drive. Or perhaps disconnect the PLG and try open loop again. Maybe you didn't follow the right procedure. Also, look at the feedback parameters as a long shot.

  4. #4
    Join Date
    Mar 2009
    Posts
    109
    Does the spindle attempt to rotate in open loop or doesn't rotate at all?? How about closed loop, does it attempt to rotate?? Since you're blowing IGBT's it may be possible you have an open phase between the motor and drive. Check for continuity in the motor cable.

  5. #5
    Join Date
    Mar 2007
    Posts
    76

    Update

    Thanks for the repsonses. The spindle will not run in open/closed loop. I also tried a new PLG card/sensor; also adjusted original several times. No help. I tried a new SF-BS card. No help. Since the SF-CA card ran another spindle, I bit the bullit and pulled the entire drive. It's on it's way to Mits. I will keep you posted.

Similar Threads

  1. Yaskawa Servopack error: A.D1. Motor Load Position Excess Error
    By Syphonics in forum Servo Motors / Drives
    Replies: 0
    Last Post: 04-26-2012, 07:53 AM
  2. alarm 55 Z SERVO LAG EXCESS.
    By EliseoMonteverd in forum Mazak, Mitsubishi, Mazatrol
    Replies: 18
    Last Post: 05-14-2011, 03:50 PM
  3. Replies: 6
    Last Post: 01-14-2011, 05:16 AM
  4. Alarm 410 V axis Excess Error, FIX?
    By D_Flannery in forum Fanuc
    Replies: 1
    Last Post: 01-14-2011, 05:13 AM
  5. Fanuc 21i 411 excess error
    By ceilingwalker in forum Servo Drives
    Replies: 1
    Last Post: 03-18-2010, 06:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •