    Anyone have experience with a Hitachi SJ200 VFD smoking

    Had a new Hitachi SJ200 VFD smoke this past weekend following a couple of successful (uneventful) initial test-runs.
    The unit smoked immediately upon power-up but had run several minutes the day before without issue - the drive has a total of less than 15 minutes time on it... Appears that an internal power resistor smoked (most likely part of the inrush limiting circuitry)... A google search revealed at least one other person looking for the EXACT SAME part for a Hitachi VFD on a Polish electronics forum... Also have seen other posts here on CNC zone where there may have been similar circumstances (although some involved questionable connections & didn't work upon 1st power-up checks).

    Thanks,
    Chris

  2. #2
    Join Date
    Jan 2005
    Posts
    15362
    sierra4sport

    Can you do a photo of your input power connections, are you using single phase 220V or 3 phase
    Mactec54

  3. #3
    Join Date
    Jan 2006
    Posts
    7
    Hi,

    Input power: 240VAC between L1 & L3/N... I read the manual AND the discussions here...

    Chris

  4. #4
    Join Date
    May 2007
    Posts
    74
    So your running 3 ph 240? Could have a high leg of the 3 ph connected to a place you would not want it connected to, especially controls.
    Jeff's CNC Plasma Cutting

  5. #5
    Join Date
    Jan 2005
    Posts
    15362
    sierra4sport

    why I asked for a photo is I think you have wired the input power to the wrong terminals, when you said you wired L1 & L3/N it should be R/L1 & T/L3 they do have some different labeling of terminals on some of the different models, But should not be on the L1 & L3/N terminals

    Your wires should be on the same level of terminals as what the motor wiring is on, if they are not then you will smoke the drive

    If your wiring is correct then you should be sending it back for repair or replacement
    Mactec54

  6. #6
    Join Date
    Jan 2006
    Posts
    7
    Hi Jeff & 'Mactec54' - Single phase AC, connected to the correct terminals - I'm not near the drive right now, so won't be taking any pictures.
    The drive was connected correctly, ran the motor a couple of start-stop cycles with varying frequency.... No changes, the next day the unit
    smoked upon power application. Hitachi says 18mo warranty from date of purchase - I'm asking them to make an exception since the unit is
    'new' (purchased and sat on shelf) - hour counters will show total hours under power are zero (assuming the 5-10 min max run time on Saturday
    doesn't 'round up' to 1hr).

    Chris

    P.S. Refer to pg 2-20 of the manual: http://www.clrwtr.com/PDF/Hitachi/Hi...-AC-Drives.pdf (one source)

  7. #7
    Join Date
    Dec 2003
    Posts
    24221
    Hitachi state that L1/R and L3/T is to be used for 1ph, if the phase loss detection was activated, L3 can be jumpered to L2, to prevent the alarm.
    The only reason for the N is for countries that have 240v 1ph and Neutral such as Australia & UK etc.
    As far as the VFD is concerned, there is absolutely no difference.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  8. #8
    Join Date
    Jan 2005
    Posts
    15362
    sierra4sport

    If you wired it to the PDF page 2-20 that is incorrect

    2-19 is the correct way to wire it, if you wired it as PDF page 2-20 you will get smoke from the drive
    Mactec54

  9. #9
    Join Date
    Dec 2003
    Posts
    24221
    BTW, the N I was referring to is the occasional use of N where the L3/T label is, NOT the N label BELOW the R,S,T, inputs.
    Some are misleading.
    Al.
    Attached Thumbnails Attached Thumbnails Hitachi_1ph-3ph.pdf  
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  10. #10
    Join Date
    Sep 2008
    Posts
    25
    Hitachi SJ200 Series has been obsolete at least for 5 years. Current comparable model is WJ200.

  11. #11
    Join Date
    Jan 2006
    Posts
    7

    Hitachi SJ-200 repaired

    Turns out the initial diagnosis for the failure was correct - 'smoked' inrush limiting resistor...
    The resistor was 'toast' - it was a 'hybrid' device, has both a resistor and thermal fuse built-in.
    Was able to obtain a replacement resistor and replace the smoked unit. Drive functions as
    intended... Has been installed on vertical mill setup & is working fine. If anyone else has
    this same failure mode on this model inverter, let me know - maybe I can help you get your
    inverter working again.

Similar Threads

  1. Hitachi SJ200-015NFU2 braking question
    By arvidj in forum Phase Converters
    Replies: 15
    Last Post: 08-12-2011, 10:47 PM
  2. Smoking x servos
    By Jig Maker in forum K2CNC
    Replies: 8
    Last Post: 02-19-2011, 09:56 PM
  3. Smoking spindle??? (oh my goodness)
    By willio in forum Shopmaster/Shoptask
    Replies: 1
    Last Post: 06-15-2009, 02:34 PM
  4. Hitachi SJ200?
    By Rich05 in forum Phase Converters
    Replies: 1
    Last Post: 12-03-2008, 06:46 PM
  5. Apparent issue with SJ200 & Leeson 3ph 2HP motor
    By haysys in forum Phase Converters
    Replies: 31
    Last Post: 01-14-2008, 01:04 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •