Hi good day,
someone has an idea on how to bypass a NPN N.O Prox Switch? Well I have a Mitsubishi FX1s-30MR PLC.. Im planning to bypass the Prox Switch..
Hi good day,
someone has an idea on how to bypass a NPN N.O Prox Switch? Well I have a Mitsubishi FX1s-30MR PLC.. Im planning to bypass the Prox Switch..
What do you mean by 'By pass?'
Jumper it out or replace with a different style, 2 wire prox or L.S. etc?
Al.
CNC, Mechatronics Integration and Custom Machine Design
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Al,
either jumper it out or cancel it from my Mitsubishi PLC.. or much better to jumper it just for a while..cause my prox is broken..
I just realized this a PLC not CNC, I have programmed the The FX-s and they come configured with optional pull up or pull down.
I am not sure if you can access the Mits site where you are, but the manuals are all on the MEAU site if you need them.
But if this is a NPN, the the input is source, so you should be able to jumper from the Prox Input terminal to 24 -ve or common.
This will simulate an ON condition.
Al.
CNC, Mechatronics Integration and Custom Machine Design
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
there are 3 wires on it, brwn (+), black, blue(-). just to be sure and clarification ,you want me to connect/jumper black and brown (+) or black and Blue(-) .then that connect to PLC? 'cause i already remove the Prox
Remove the prox completely and just use a single jumper from the prox input to the 24v common terminal, this is usually supplied from the PLC for inputs.
This would have been the BLK & Blue on the original.
Al.
CNC, Mechatronics Integration and Custom Machine Design
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Al,
thanks a lot, you save the day. thanks for your help..