Hello Daniel,
We would like to echo and add to what Ray has stated. The stand wiring can be connected as indicated in the attached picture. The Blue set of wires are used for the spray down pump and are connected to the 220VAC terminals and is controlled from the switch on the front of the stand.The red wires are connected through the SSR and the 220VAC terminal also as indicated. The SSR is activated via the flood control in Mach3.
The hum in the X axis can be controlled by adjusting the "position feed back gain" parameter P009 on the servo driver. You can lower this (maybe in increments of 5) until the hum goes away. The default factory setting is 40 and we may have made some adjustments to this already before it was shipped. We would have lowered it to just above the threshold. The X axis seems to be the only axis usually needing adjustment.
If unplugging the sensors does not stop the E-stop triggers, try unplugging the N.O. soft stop plug from the BOB and see if it false triggers. The E-stop button will still control the hard stop since it will cut off the driver power via the power relay. This will indicate if the triggers are originating from the E-Stop cabling.
Regards,
Novakon Team
Make sure you follow the write to EPROM procedure in the drive manual otherwise the setting won't save. But me yesterday when I was changing a wrong parameter on my servo drive.
Nate