    Sep 2006
    177
    Question Wye-delta, delta-wye configurations?
    I recently setup a CNC rotery phase converter, and i want to make sure the type of power output is what i need for AC brushless servo motors. I read something in the phase converter manual that said "if u need a four-wire wye voltage output, a delta-wye transformer is needed". I'm not sure what this is or if i need it. I beleve the 3-phase power from the phase converter is right, but i want to make sure before i hookup my motors. Anyone know anything about these delta-wye, wye-delta, wye-wye, and delta-delta configurations and how are they related to the input power for AC brushless 3-phase servo motors. thanks
    Aug 2006
    2758
    Are you planning to run the AC Brushless servo motors from the rotary phase converter directly? No servo controller in between?
    24221
    AC brushless permanent magnet servo motors will not run off of mains three phase directly, they require commutation.
    The drives convert the incoming AC to DC and then manufacture electronically the three phases and receive commutation signals from the motor.
    If you are concerned about the AC power to the drives, it does not matter if the 3 phase is delta or star (Wye), as long as it is the right voltage.
    Al.
    Albert E.
    Aug 2006
    2758
    I asked what his intention is because I want to make sure mackeym don't damage his motors by connecting them directly to the three phase line.
    Sep 2006
    15
    getting back to the original question, the Delta Star connected transformer provides a neutral connection from a 3 wire supply
    the Delta primary consists of 3 coils all rated at the supply voltage, so in the UK that's 415V. each winding is connected directly to two input phases
    The Star secondary consists of three windings rated at 240V. the starts of all three windings are joined together (forming a star point, neutral) and then the three limbs radiate out at 240V each. from one tip of the star to the next you will measure 415v
    a factor of '/3 (root 3)
    it'll never work. it'll never be finished. more fun than watching a soap though
    Sep 2006
    177
    opps. forget to mention that I'm going to use a pacific scientific sc900 series drives.
    24221
    if you set up a RPC for these drives, then it would be equivalent to 3 phase Star connection, But without the star point being available.
    But you don't need it.
    You could feed these drives with either configurations, (star or delta).
    The star connection normally gives you a neutral or common as Grim pointed out, which as I say, you don't need.
    Don't they also take single phase? I know the SC750's do.
    Al.
    Albert E.
    Sep 2006
    177
    there are different sizes...sc902, sc903, sc904, and sc905.....the sc902 and sc903 take either single or three phase. the sc904 and sc905 take only 3 phase.
    24221
    Your RPC output should be OK as long as the voltage is within the correct limits.
    Al.
    Albert E.
    Sep 2006
    177
    ok, thanks. yeah, the voltage is in the right range. this RPC has a voltage balance of 5% (CNC phase converter). I was wondering if voltage imbalance even has a large effect on performance since the drive first converts the power to DC.
    24221
    Quote Originally Posted by mackeym View Post
    Your right, you probabally won't even notice it.
    Al.
    Albert E.
    Apr 2006
    10
    Hi just got an SC903 but can't find a wiring diagram for single phase. Do you have one?
    Sep 2006
    177
    Re: Wye-delta, delta-wye configurations?
    The manual is available on Kollmorgen's website (http://www.kollmorgen.com/uploadedFi...900_Manual.pdf).
  1. I NEED HELP (DELTA 20 PU)
    By nice-day in forum Dynapath
    Last Post: 12-13-2012, 07:50 PM
  2. delta G41 G42
    By LVX in forum SIEMENS -> GENERAL
    Last Post: 07-18-2011, 09:27 PM
  3. Delta VFD -E help
    By woodguy60 in forum Phase Converters
    Last Post: 03-19-2010, 04:47 PM
  4. Delta Tau
    By Leblondmakino in forum CNC (Mill / Lathe) Control Software (NC)
    Last Post: 04-30-2008, 05:07 AM
  5. delta 40
    By rhurt in forum Tree
    Last Post: 03-25-2007, 04:33 AM