    Fanuc 18i-MB parameter write protected

    please help have had to do a memory clear on my T21i-D so now need to re enter my O9000 programs

    I have changed PWE to 1 then turned off and back on again but when I try to change parameter 3202 bit 4 (NE9) from 1 to 0 I get a WRITE PROTECTED alarm

    how do I get over this

  2. #2
    Join Date
    Jun 2004
    Posts
    511

    Re: Fanuc 18i-MB parameter write protected

    I have changed PWE to 1 then turned off and back on again?

    Put PWE to one and just leave it on, you must be in MDI to edit parameters. Some machines also need to be in Estop.

  3. #3
    Join Date
    Jan 2015
    Posts
    3

    Re: Fanuc 18i-MB parameter write protected

    thanks ifixcnc the book says after changing PWE to power of and on

    still no joy

  4. #4
    Join Date
    Jun 2004
    Posts
    511

    Re: Fanuc 18i-MB parameter write protected

    Call Fanuc Tech Help 1-888-326-8287 they should know what to do. I have dont have a 21i-D

  5. #5
    Join Date
    Jan 2015
    Posts
    3

    Re: Fanuc 18i-MB parameter write protected

    sorry located in the UK

  6. #6
    Join Date
    Jan 2015
    Posts
    2

    Re: Fanuc 18i-MB parameter write protected

    Put the emergency stop and then you try to change the parameters.

  7. #7
    Join Date
    Aug 2011
    Posts
    2517

    Re: Fanuc 18i-MB parameter write protected

    leave PWE on 1 and DO NOT power off. if you power off, the machine will re-set PWE to 0.
    Set mode to MDI, Set PWE to 1, change the parameters then after you have finished, power the machine off then on.

  8. #8
    Join Date
    Mar 2003
    Posts
    2932

    Re: Fanuc 18i-MB parameter write protected

    1. MDI - Settings - PWE=1 (Alarm P/S100 flashes as warning that PWE is ON... you can ignore this).
    2. System - PARAM - key in 3202, press [NO. SRH] - cursor over to bit 4 and set it = 1.
    3. Go back to Settings and turn PWE = 0, then RESET to clear the alarm - no need to power off.

    Re-enter O9000 programs.

    After you've finished, repeat steps 1, 2 (set 3202 bit 4 = 0, and 3 - still no need to power off.

Similar Threads

  1. Replies: 4
    Last Post: 06-06-2023, 04:27 AM
  2. Replies: 3
    Last Post: 08-22-2014, 08:13 AM
  3. Replies: 3
    Last Post: 04-16-2012, 06:12 PM
  4. write protected dwg
    By smudger in forum Autodesk
    Replies: 9
    Last Post: 09-05-2007, 08:26 PM
  5. write protected
    By stevieboy in forum Autodesk
    Replies: 5
    Last Post: 06-03-2004, 09:03 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •