    Exclamation Limit switches question

    Sorry if this is not the right thread.
    Having read many threads, all recommend 6 limit switches for a gantry router/mill. One on each end.
    Does anyone see any problem with single switch on each axis activated by a ramp at each end. The switches connected in series.
    The switch having a roller and the ramps adjustable to set the limit positions.
    I will be using Mach3 and a HobbyCNC controller
    The More I Learn The Less I Seem To Know

  2. #2
    Join Date
    Apr 2004
    Posts
    90
    One overtravel limit switch per axis with two ramps per switch will work just fine as you have described. If you wire them in series, I would recommend that you use the normally closed contacts so that all switches make a complete chain in series, and opening a single contact would break the chain and trip the overtravel input. (Perhaps you had this in mind already, I was just checking)

    Brian

  3. #3
    Join Date
    Jun 2005
    Posts
    199

    Smile Thanks

    Thanks for the reply,
    I could not see any gremlins but experience is always useful even if it is someone else's.
    The More I Learn The Less I Seem To Know