So you are trying to go form 60Hz machine & want to run it on 50Hz, something like this might get you going
http://www.aliexpress.com/item/High-...364443976.html
There is lots of information on this, most suggest, to contact the manufacture, to see if they have the 50Hz rated parts, then change out those parts, that will suit the voltage frequency you have, here is a little information of what is happening that may help also
IF it was the other way round, and you had a 50 Hz machine, and want to run it on 60 Hz this is a little easier to do
50HZ Appliance & 60HZ Power Supply and vice versa
A 50 HZ power supply is common used in Europe while a 60 HZ power supply is common used in USA, Typically most of the electrical loads have a frequency range they are compatible with and it is common to see that the range span is from 50 HZ to 60 Hz
What is the difference between 50 HZ and 60 HZ power transformer
Transformer which made for 60 HZ is smaller than transformer made for 50 HZ , but in some cases they are in the same size and in this case the 60 HZ version will use lower grade steel laminations which mean it will be cheaper than the other
Can we connect 60 HZ power transformer to 50 HZ power supply
If you make this the transformer will get much hotter than normal and easily reach to a dangerous temperature that will cause transformer failure, this is because the transformer primary number of turns is designed according to input voltage to input frequency ratio (V/F) so if the frequency is reduced then (V/F) ratio will increase and there will not be sufficient number of turns to prevent transformer from reaching core saturation, So transformer will draw much more current from the main's getting hotter leading to failure
Can we connect 50 HZ power transformer to 60 HZ power supply
Yes, you can and you will rarely have a problem as operating a 50 HZ transformer on 60 HZ power supply reduces the drawn current and hence the transformer will run a little cooler
?Can we connect 50HZ induction motor to 60HZ Power Supply or vice versa
If I connect a 60 HZ induction motor to a 50 HZ power supply, the motor will draw more current and run at lower speed and if I connect a 50 HZ induction motor to a 60 HZ power supply the motor will draw lower current and run at high speed and in the two cases the result is excessive heat
.buildup inside the motor that strongly shortened motor operating life
How can you safely operate a 60 Hz appliance at a 50 HZ power supply or vice versa
:You should follow the following steps
First: contact the appliance manufacturer as it may be possible to safely
.operate your appliance with the manufacturer approval
Second: some manufacturers sell the same appliance in 50 HZ and 60 HZ
.countries, so try to connect manufacturer as he may have a solution
Third: you can purchase 60 HZ sine wave power supply but this solution is generally very expensive and it will be more cost effective to replace