586,075 active members*
3,595 visitors online*
IndustryArena Forum > CNC Electronics > CNC Machine Related Electronics > Npn NO proximity sensor question.
Page 1 of 2 12
Results 1 to 20 of 22
    Feb 2016
    29
    I have a concern regarding my npn NO sensors. I have them wired up in parallel with a resistor to drop 12v input to 5v. I have the resistor from -12v (blue wire) jumped to output (black wire). All works good, drops voltage to 4.9v. However, when sensor is triggered it drops to 0.75v instead of 0.0v as I would expect it to. Is that normal? Will that 0.75v fry my c10 BOB?
    Sent from my SM-G950W using Tapatalk
    May 2015
    686
    Re: Npn NO proximity sensor question.
    You may need to add a pull down resistor
    Rod Webster
    www.vehiclemods.net.au
    Dec 2017
    77
    You shouldn't need any negative voltages. Connect blue to ground and connect brown to your positive voltage supply.
    Connect a load resistor between brown and black. The value should be high enough that the current, from I = V/R, is less than the rated load current for the sensor. In this way, you can use any positive voltage that is within spec for the sensor, as the supply. Now, the black will be either at V+, with impedance R, or shorted to ground. I'm not sure why you're measuring 4.9v. That doesn't sound right.
    If you were to then convert that output to 5V levels using just a resistor, you would get something like you describe. Perhaps that's the case, as your sensor has a built-in load resistor, and you added a resistor between black and the BOB?
    The correct way is to use a second transistor to shift the level. However, if you've got something that works, you're good. Digital inputs have very high input impedance. It means that, no matter if it's 0.75 V or 5V or whatever, very little current is flowing.
    Mar 2007
    2083
    what is the part number of the Npn NO proximity sensor ?
    usually the sensor has an open collector output
Name:	no npn proximity switch.jpg
    so you will only need to set the jumper on the C10 BOB's input pullup / pull down resistor to pull up
    in practice the C10 BOB's input should be between 0V & the +5V supply
    (the absolute limits - 0.6V & +5.6V any more or less will forward bias the 74ACT245 input protection diodes )
    circuit details of the C10 taken from the manual and traced from online photos
    Attachment 391456
    sensor to C10
Name:	no npn proximity switch & C10.jpg
    John
    Dec 2017
    77
    Ah yes, with no load resistor it is open collector output. That should have been obvious, doh!
    Yes, in that case it can be done right with no extra transistor. You activate pull-up on the C10, and it gets switched to ground when activated.
    Feb 2016
    29
    Hi. The is the proximity sensor I'm using.
    LJ12A3-4-Z/BX Inductive Proximity Sensor Detection Switch NPN DC6-36V 4mm Normally Open Proximity Switch.
    Im using a resistor to lower voltage to 5v but its jumped across blue and black wire. Should it be from brown wire instead? Do I even need the use of a resistor? I'm a noob when it comes to these switches.
    Thanks for the help thus far.
    Dec 2017
    77
    Lowering voltages is not what resistors do. They set the voltage to current relationship. Spend some time with ohm's law and the voltage divider equation, and it may start to make sense.
    You can take it out, and use the pull-up on the BOB. In this case, a "load resistor" gives an output at the level of the sensor power supply, which is too much. A "pull-up resistor" is essentially the same thing, but on the BOB side, which has a different voltage powering all the logic, so that way our sensor output only goes up to 5 volts.
    The only thing the sensor does is defeat the pull-up by grounding the output.
    Feb 2016
    29
    Ok. That makes sense now. That's for the help. I'll remove the resistor and wire directly to BOB. Thanks for the help.
    Mar 2007
    2083
    while I have been looking for a detailed data sheet for the LJ12A3-4-Z/BX Inductive Proximity Sensor
    (so far I have failed to find the details I was looking for )
    jo_ky has said in post 7 what I indicated in the 3rd diagram in post 4
    sensors with NPN open collector outputs will not provide any voltage or current and can only sink current
    from the likes of an onboard pull up resistor on your C10 BOB
    John
    Feb 2016
    29
    This is the wiring diagram for two NPN NO sensors in parallel from the c10 BOB manual. I confused as to why it says to use a resistor if its integrated into c10 BOB.
    Apr 2003
    540
    Just a little info for what it's worth.. I went through some of the same issues as you are regarding proximity sensors. Mine are 10-30 volts. I'm ok with electronics, but not a wiz. I was finally able to figure it out using resistors etc, but changed the setup by simply using an 8 channel 24 volt relay module that's optocoupler isolated and allows you to pull high or low on each relay as needed. You can also get 12v (or other voltages based on your proximity sensors and power supply available). They are only about $10 and make the sensors much easier to wire and connect to any breakout board and eliminates all the resistor mess and lowering voltages. You likely don't need an 8 relay one, but having a spare/extras if needed down the road for something else may be well worth the tiny difference in price.
    Mar 2007
    2083
    the diagram in post 10 is correct when the proximity sensors have internal pull up resistors and are being powered from a supply that's higher than the 5V supply to the C10 BOB
    Attachment 391510
    John
    PS
    since I have not found a detailed data sheet for the proximity sensor
    it may be worth testing to see if the sensor has a true open collector output
    I would connect your 12V supply 0V to the blue common / 0V and
    +12v to the brown + supply
    if the sensor has an NPN open collector output then you should not have any voltage
    between the blue common and black output when the switch is either off or on
    if the sensor has an internal pull up resistor or LED indicator between the brown + supply
    and black output
    then you will measure a voltage between the blue common and black output when its switched off
    Feb 2016
    29
    Not surprising you can't find any data on them. They are those cheap Chinese ones from Amazon.
    I did the suggested test. I measure +12v across blue and black wires. When sensor is triggered I get +0.75v. My test is with two sensors I'm parallel.
    Mar 2007
    2083
    for the 74ACT245 used on the C10 BOB
    +0.75V is low enough to be a valid logic 0 (LOW)
    so that's OK when the proximity switch is on
    when all switches are off
    +3.5V or more will be a valid logic 1 (HIGH)
    what doe you measure when all proximity switch outputs are off ?
    John
    Feb 2016
    29
    It measures +12.38v when off.
    Feb 2016
    29
    A little off topic but will all the different voltage is have, 48v, 12v, and 5v, should I be using the -48v ground for all negative connections?
    Mar 2007
    2083
    +12.38V implies either you have
    a proximity switch with a pull up resistor between the positive 12V supply and the open collector NPN output
    so the output is high (+12V) when switched off
    which is what a LJ12A3-4-Z/BX proximity sensor is
    or
    you have a proximity switch with a PNP output that connects the output to the positive supply when switched on
    John
    PS
    to answer post 16
    assuming the 48V supply is for your stepper drivers , 12V for your proximity switches and 5V supply for the C10 BOB
    then
    you can connect all the negative terminals together
    note -
    when the C10 is connected to a desktop PC printer port
    the negative supply terminal will be connected to the mains supply earth / ground
    via the PC power supply
    the PC AT (or ATX) black 0V connections will connect the motherboard common including all the I/O connectors to earth
    Dec 2017
    77
    To be clear, the test has to be done with everything else disconnected. That's the case?
    I would also check if there's any change in the voltage levels depending on whether it's one or both closed.
    Mar 2007
    2083
    with two or more switches in parallel
    as soon as one switch closes the voltage will drop to near 0V
    with your results I can see why the connection diagram for the C10 BOB ( posts 10 & 12 )
    a resistor is connected between the proximity sensor output (black wire) and C10 input
    with a 12V supply the manual gives the total resistance for the pull up resistor between the +12V supply and output plus the resistance connecting the sensor output to the C10 input as 10K
    with the C10 input jumper set for a pull down 4K7 resistor
    the volt drop across the 4K7 resistor & BOB input would be
    4.7 divided by 14.7 times 12V = 3.8V which is more than the minimum of 3.5V for a logic 1 input
    with proximity switches in parallel the resistance between the +12V supply and the paralleled outputs will depend on how many switches are in parallel
    with no details of the proximity switch available
    you could connect the sensor outputs to ground / 0V via a 1K resistor
    and use the voltage across the 1K resistor to work out what resistance you have between the +12V supply and the sensor outputs
    subtracting the result from 10K to find the value of the resistance needed between the sensor outputs and G10 input
    John
    Feb 2016
    29
    Ok. I got the two proximity sensors wired in parallel to output 4.47v when triggered. However, mach 3 is not recognizing the sensor when I trigger it. I tried setting the pin jumper on c10 BOB to pull up and to pull down... nothing. I tested the BOB inputs for the proximity sensor and they read 5.5v whether I have pin jumper to pull up or pull down. I followed this diagram. I'm confused.
Page 1 of 2 12
  1. Proximity sensor wiring
    By Lindzr in forum Automation Technology Products
    Last Post: 08-16-2017, 01:29 AM
  2. CRP's Proximity Sensor Kit
    By rwskinner in forum Avid CNC
    Last Post: 02-12-2014, 04:07 AM
  3. BB does not read +5 from proximity sensor
    By crane550 in forum DIY CNC Router Table Machines
    Last Post: 03-25-2012, 02:01 PM
  4. proximity sensor issue
    By strohkirchw in forum Benchtop Machines
    Last Post: 05-27-2011, 10:14 PM