586,378 active members*
2,543 visitors online*
IndustryArena Forum > Machine Controllers Software and Solutions > Dynomotion/Kflop/Kanalog > Kflop/Kstep to G0704 KBIC spindle speed control help.
Results 1 to 12 of 12
    Feb 2016
    13
    Currently I have connected JP33 Pin 7 to KBIC P3 and JP33 Pin 5 to KBIC P1 on Kstep. Measuring voltage across Pin 5 and 7 I have 11.09V, From Pin 6 to Pin 7 I have 3v instead of 5V. From this point I'm not sure what my next step is.
    #include "KMotionDef.h"
    #include "CorrectAnalogFunction.c"
    #define RefVoltage 11.09f
    main()
    float V=5.0;
    FPGA(KAN_TRIG_REG)=4; // Mux PWM0 to JP7 Pin5 IO 44 for KSTEP
    SetBitDirection(44,1); // define bit as an output
    FPGA(IO_PWMS_PRESCALE) = 46; // divide clock by 46 (1.4 KHz)
    FPGA(IO_PWMS+1) = 1; // Enable
    FPGA(IO_PWMS) = CorrectAnalog(V/RefVoltage); // Set PWM
    Feb 2016
    13
    Re: Kflop/Kstep to G0704 KBIC spindle speed control help.
    Do I need to add this C program to get my voltage corrected, or am I missing something else?
    // PWM->Analog Correction
    // assume very non-linear for first few count and linear thereafter
    // Measure output ratio for first 0-7 counts then at 240
    float V[]=
    0.001, // count = 0
    0.031, // count = 1
    0.044, // count = 2
    0.054, // count = 3
    0.062, // count = 4
    0.069, // count = 5
    0.074, // count = 6
    0.079 // count = 7
    float V240=0.970;
    int CorrectAnalog(float v)
    int r;
    float v2=2.0f*v;
    // compare with half way points to determine closest count
    if (v2 < V[1]+V[0]) return 0;
    if (v2 < V[2]+V[1]) return 1;
    if (v2 < V[3]+V[2]) return 2;
    if (v2 < V[4]+V[3]) return 3;
    if (v2 < V[5]+V[4]) return 4;
    if (v2 < V[6]+V[5]) return 5;
    if (v2 < V[7]+V[6]) return 6;
    // must be 7 or higher do linear interpolation
    r = (int)(7.5 + (v-V[7])/(V240-V[7])*(240.0f-7.0f));
    if (r>255) r=255;
    return r;
    May 2006
    4047
    Hi RootbeerFLHX,
    It should be much closer to 5V. I'm not sure what is wrong. Are you sure you measured 11.09V as the supply voltage? That seems very coincidental that it was the exact default value in the file.
    Does it remain 11.09V after running the program?
    Is the output voltage measured with no load or other connections except your meter?
    If you command voltages other than 5V what do you get?
    The #include "CorrectAnalogFunction.c" statement includes the CorrectAnalog() function (code is more readable if you paste it into CODE tags from the cnczone Advanced page).
    Regards
    TK
    http://dynomotion.com
    Feb 2016
    13
    Hi Tom.
    The 11.19v on pin 5 and 7 was before the program runs. Checking with the program running it is 4.462v on pin 5 and 7, 3.472v on pin 6 and 7. I changed the RefVoltage to 4.462f, and attached pin 6 to the speed controller, but I'm still only able to get 1248 rpm with a S2500 command.
    Feb 2016
    13
    Ok, I'm not sure what I did, but now it's running at 2184 with a S2500, maybe the program needed to be restarted? Anyway, is there a way to fine tune the numbers a little closer?
    May 2006
    4047
    Hi RootbeerFLHX,
    I think you should go back and repeat the previous experiment. KStep only puts a max of a 1Kohm load on the reference voltage from the KBIC drive. The reference voltage out from the drive should remain relatively constant otherwise I suspect things will be very nonlinear. Do you have a specification on the drive?
    Regards
    TK
    Feb 2016
    13
    Specs on the board are:
    Model: JYMC-220B-II
    Input: 115VAC-50/60 HZ
    Output: 0-90 VDC
    Rated: 13.5 ADC
    Yangzhou Jiayi Mechano-electronics Institiute
    Feb 2016
    13
    the original Potentiometer is 4700ohms.
    May 2006
    4047
    Hi RootbeerFLHX,
    Can you find a link to the full manual including the analog Reference output voltage specification and analog input requirements?
    Regards
    TK
    Feb 2016
    13
    http://www.kbelectronics.com/manuals/kbic_manual.pdf
    KBIC-125 is very similar to what I have. I have been unable to track down a manual using the other part number.
    Dec 2003
    24223
    That other part number appears to be a totally different drive to the KBIC?
    With the KBIC you should also be using the I1 & I2 terminals to inhibit if reversing etc or stopping by removing motor power, as this resets the drive and allows the drive to use the accel setting to come up to speed.
    Al.
    Albert E.
    Feb 2016
    13
    Al.
    Somewhere else I had read they were a Chinese knockoff of the KBMM or KBIC, but that's a good point about the Inhibit connections that I hadn't thought about.
  1. KStep Spindle Control Example - UserData[1] array is empty
    By kdoske in forum Dynomotion/Kflop/Kanalog
    Last Post: 12-31-2015, 02:13 AM
  2. G0704 KB120 Spindle Speed Control C41 Board
    By tpks in forum Spindles / VFD
    Last Post: 08-17-2015, 05:25 PM
  3. Mach3 + Kflop + VFD = Spindle Speed control?
    By slimneill in forum Dynomotion/Kflop/Kanalog
    Last Post: 05-07-2015, 06:22 PM
  4. C6 Spindle control for KBIC
    By zerodegreec in forum Benchtop Machines
    Last Post: 04-22-2013, 11:02 PM
  5. Spindle Control Inhibit and reversing KBIC
    Last Post: 02-14-2013, 01:05 AM