Originally Posted by
cnckeith
Marty,
- if you haven't already, set the inverter to display Hertz while running. this is a good debug too. (along with the fluke meter on the analog output of the allin1dc) to quickly see what the inverter is outputting when you command the spindle to spin.
- make sure the spindle overide button on the operator panel is set to 100%
- verify that the analog output adjustment switches are set to the 0-10 vdc setting a per the install manual as well. (fyi.. the allin1dc can be set to output 0-10vdc, 0-5 vdc, +-10vdc or +-5vdc for the spindle control output via the dip switches on the allin1dc and the plc program).