    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Quote Originally Posted by Eldon_Joh View Post
    from what i can tell, it is the motors that are specified as 200 volts, not the drive, which makes sense because you need additional headroom, i think the drives are intended to run off of 240vac, but i can't find it in the literature.

    anyhow, these are modern drives, they will run off of single phase. the only question that remains is can they handle full output while doing so.

    additionally, the drive has to compensate for higher ripple voltage, the manufacturer may not want to deal with the headaches associated with guaranteeing their drives can meet the advertized specifications while running on single phase.
    All the Yaskawa servo drives are 100v series 200v series 400v series +/- 10% with matching Servo Motors of the same Voltage, why are you posting incorrect made up information

    The Servo Drives he has is 3Ph and list a Phase sensor for each Phase so can not be run on single phase unless you know what to do to get around the Phase sensor

    It also list that this Servo Drive 3R8A can not run on Single Phase
    Mactec54

  2. #22
    Join Date
    May 2013
    Posts
    480
    Quote Originally Posted by mactec54 View Post
    All the Yaskawa servo drives are 100v series 200v series 400v series +/- 10% with matching Servo Motors of the same Voltage, why are you posting incorrect made up information

    The Servo Drives he has is 3Ph and list a Phase sensor for each Phase so can not be run on single phase unless you know what to do to get around the Phase sensor

    It also list that this Servo Drive 3R8A can not run on Single Phase
    So answer the question... why can't it run on single phase. edit: (providing of course he can fool the phase sensor, which your motor starter will not do, and if it can, then the servo drive phase loss detector isn't a phase loss detector, but a bull**** loss detector.)

    Also, with one exception I think, there is no 200v 3 phase power grid anywhere. So Op will need a rotary phase converter and two or three 32v transformers to drop his 240v grid to 208vac 3 phase.


    Additionally, while it appears the servo drive has the capability of feeding forward the 120/100hz ripple that will appear on the dc bus into the pwm algorithm, it wouldn't surprise me if the manufacturer simply doesn't want to guarantee that it can meet performance specifications one single phase, three phase of course has something like a tenth of the dc ripple to deal with.

    If the servo drive was really intended for a 200v power grid 240v may be too high. If it isnt, then it will run off 240v single phase for certain. But there is a slim possibility there is a 3 phase PFC front end that will not work with single phase, and if that is the case, your 50$ motor starter will not work either, and you know they don't generate three phase.

  3. #23
    Join Date
    Jan 2005
    Posts
    15362

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Quote Originally Posted by Eldon_Joh View Post
    So answer the question... why can't it run on single phase. edit: (providing of course he can fool the phase sensor, which your motor starter will not do, and if it can, then the servo drive phase loss detector isn't a phase loss detector, but a bull**** loss detector.)

    Also, with one exception I think, there is no 200v 3 phase power grid anywhere. So Op will need a rotary phase converter and two or three 32v transformers to drop his 240v grid to 208vac 3 phase.


    Additionally, while it appears the servo drive has the capability of feeding forward the 120/100hz ripple that will appear on the dc bus into the pwm algorithm, it wouldn't surprise me if the manufacturer simply doesn't want to guarantee that it can meet performance specifications one single phase, three phase of course has something like a tenth of the dc ripple to deal with.

    If the servo drive was really intended for a 200v power grid 240v may be too high. If it isnt, then it will run off 240v single phase for certain. But there is a slim possibility there is a 3 phase PFC front end that will not work with single phase, and if that is the case, your 50$ motor starter will not work either, and you know they don't generate three phase.
    I think that is already clear,what I posted, what will stop it from running, but I have a way around that

    His 220v Power supply is in the range to safely connect it direct to the Servo Drive, I have connected Yaskawa Drives with the 240 Us single phase without any problems, so the Drives are very tolerant,of the supply voltage, they are the Industry standard, and the most sold servo system in the world

    Nobody said the the Static phase converter generates 3 Ph power, but will trick the servo drive to thinking it has a 3ph supply, but my work around will do the same thing also
    Mactec54

  4. #24
    Join Date
    Dec 2003
    Posts
    24221

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    The Phase Perfect produces true 3phase from single phase input, with in 1% of mains frequency, the two single phase lines are passed directly through and produces the 3rd phase from these.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #25
    Join Date
    Jan 2005
    Posts
    15362

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Quote Originally Posted by Al_The_Man View Post
    The Phase Perfect produces true 3phase from single phase input, with in 1% of mains frequency, the two single phase lines are passed directly through and produces the 3rd phase from these.
    Al.
    Yes they do I have one,expensive but worth it if you need a good 3 Ph supply, the static phase converters I suggested only makes a fake 3rd leg, which most times is enough to get things running, not perfect but does what is needed
    Mactec54

  6. #26
    Join Date
    Dec 2003
    Posts
    24221

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    I made my original RPC from the Fitch Williams design from the '80's it produces three phase but not very stable as far as exact frequency, but pretty close as Fitch's 'scope picture of the 3 relative phases showed. Good enough for VFD's and 3 ph motors etc.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  7. #27
    Join Date
    Dec 2006
    Posts
    130

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    hi, i am facing this issue, powering up a 3phase yaskawa servo driver using a 1ph power.
    Am i able to connect a capacitor for the 3rd leg power? similar to powering a 3phase motor using a 1ph power.

  8. #28
    Join Date
    Jan 2005
    Posts
    15362

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Quote Originally Posted by Syphonics View Post
    hi, i am facing this issue, powering up a 3phase yaskawa servo driver using a 1ph power.
    Am i able to connect a capacitor for the 3rd leg power? similar to powering a 3phase motor using a 1ph power.
    No don't do that you will damage the drive

    What Servo Drive do you have model spec's
    Mactec54

  9. #29
    Join Date
    Dec 2006
    Posts
    130
    The driver is SGDM 08ADA

    Quote Originally Posted by mactec54 View Post
    No don't do that you will damage the drive

    What Servo Drive do you have model spec's

  10. #30
    Join Date
    Jan 2005
    Posts
    15362

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Quote Originally Posted by Syphonics View Post
    The driver is SGDM 08ADA
    The only way you can Power this up with Single Phase

    Is Power connection to L1 and L2 and a Jumper from L1 to L3

    So Live / Hot wire on L1

    So try it with just L1 and L2 connected if you get a Phase Loss Fault then you can Jumper L1 to L3
    Mactec54

  11. #31
    Join Date
    Dec 2006
    Posts
    130

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Quote Originally Posted by mactec54 View Post
    The only way you can Power this up with Single Phase

    Is Power connection to L1 and L2 and a Jumper from L1 to L3

    So Live / Hot wire on L1

    So try it with just L1 and L2 connected if you get a Phase Loss Fault then you can Jumper L1 to L3

    Hi Thanks I will give it a shot, will this method fry the driver?

  12. #32
    Join Date
    Jan 2005
    Posts
    15362

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Quote Originally Posted by Syphonics View Post
    Hi Thanks I will give it a shot, will this method fry the driver?
    No it will not fry the drive, it is the only way to run it on Single Phase
    Mactec54

  13. #33
    Join Date
    Dec 2006
    Posts
    130

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Thanks I will try that out.
    But I can’t understand why does shorting L1 and L3 allows the driver to run with 1 phase?
    Does it affect the output power or torque?


    Sent from my iPhone using Tapatalk

  14. #34
    Join Date
    Jan 2005
    Posts
    15362

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Quote Originally Posted by Syphonics View Post
    Thanks I will try that out.
    But I can’t understand why does shorting L1 and L3 allows the driver to run with 1 phase?
    Does it affect the output power or torque?


    Sent from my iPhone using Tapatalk

    It is not shorting anything it is providing a power presence to fool the phase loss detection circuit

    Of cause it will affect the motor performance, you are still only using Single Phase supply, if the Drive is the same size as the motor you will need a derating by 1/3 or 1.73 for the lost amps that would normally would be available from the missing phase
    Mactec54

  15. #35
    Join Date
    Dec 2006
    Posts
    130

    Re: 220V single phase VFD 3 phase output for powering a 200V 3phase AC Servo drive/mo

    Thanks mactec54, it does works.


Page 2 of 2 12

Similar Threads

  1. Bridgeport R2E3 delima, 220v VFD 3 phase Versus 220V Single Phase
    By ronderkis in forum Bridgeport / Hardinge Mills
    Replies: 7
    Last Post: 03-25-2015, 04:01 AM
  2. Replies: 2
    Last Post: 06-20-2014, 05:24 AM
  3. Change a motor from 415v 3 phase to 220v 3 phase
    By Me2 in forum Phase Converters
    Replies: 3
    Last Post: 06-02-2010, 10:29 PM
  4. MultiCam Pro 3phase conversion to single phase
    By Max in forum Commercial CNC Wood Routers
    Replies: 8
    Last Post: 03-30-2010, 06:34 PM
  5. Replies: 12
    Last Post: 10-13-2009, 03:53 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •