    setting up a hypertherm 260xd

    hey guys

    i recently bought a 2 year old 260xd. i am now in the process of setting up this machine and i am having trouble finding a location that supplies enough power to run it.

    i was hoping to clarify a few questions i have on power demands of this unit.

    am i correct in saying this machine requires 75 amps per phase? or is it 25 amps per phase totaling 75 amps?

    considering it will be rare for me to use the machine at full capacity, probably most of the heavier work will be 32mm pierce cuts, what can i get away with in regards to power supply.

    one option i have is to purchase a generator to run it (not my first choice) but i was hoping someone could shed some light on their experiences with power demands

    cheers
    Ryan

  2. #2
    Join Date
    Nov 2016
    Posts
    6

    Re: setting up a hypertherm 260xd

    bump

  3. #3
    Join Date
    Mar 2016
    Posts
    59

    Re: setting up a hypertherm 260xd

    Quote Originally Posted by rhinocut View Post
    hey guys

    i recently bought a 2 year old 260xd. i am now in the process of setting up this machine and i am having trouble finding a location that supplies enough power to run it.SO, you're looking for a building that has sufficient power? where is the cutting machine set up now?

    i was hoping to clarify a few questions i have on power demands of this unit.

    am i correct in saying this machine requires 75 amps per phase? ASSUMING that your power input is 400/415 VAC - Yes, At full output 75 amps per phase, fused for 100 or 130 so at initial plasma fire you don't blow the fuses (Delta T power surge), or is it 25 amps per phase totaling 75 amps?

    considering it will be rare for me to use the machine at full capacity, probably most of the heavier work will be 32mm pierce cuts, 32mm cutting in ? Stainless? Carbon Steel? Aluminum?what can i get away with in regards to power supply.
    I interpret this as "Can I supply less current to the power supply and still use it if I run the output at FAR less than the machine is rated for" I would not recommend that, and if a client asked me to do that, I would refuse, but it's your power supply. If you cannot get a power service/building entrance upgrade for less than the cost of a 90KW generator (30KW per phase, 3 phase = 90KW) then you may want to consider either not using this power supply or finding a new location. If that isn't possible then yes, the generator will be your only option. I would think that you wouldn't want to cut 32mm carbon steel at less than 200 amps, and even at 200 amps it will be quite slow IMO. Your speed would be in OF cutting speed territory. It only gets slower if you're cutting 32mm stainless.


    one option i have is to purchase a generator to run it (not my first choice) but i was hoping someone could shed some light on their experiences with power demands
    My opinion: Feed the beast. You wouldn't ask Pharlap to run a race on half rations. It a good power supply you have. I hope you work this out

    cheers
    Ryan
    Good luck

Similar Threads

  1. How setting tools and setting offset
    By John246 in forum Sharp CNC
    Replies: 11
    Last Post: 04-09-2016, 08:31 PM
  2. hypertherm 600
    By Blowmeracing in forum Hypertherm Plasma
    Replies: 2
    Last Post: 03-06-2013, 02:08 AM
  3. Is there a setting to jog using the the G68 angle setting?
    By Smertrios in forum Mach Software (ArtSoft software)
    Replies: 3
    Last Post: 12-05-2012, 01:57 AM
  4. Hypertherm MAX 70
    By blips in forum Hypertherm Plasma
    Replies: 1
    Last Post: 06-30-2012, 03:45 PM
  5. New Hypertherm 85
    By travmc1 in forum Hypertherm Plasma
    Replies: 2
    Last Post: 05-21-2012, 02:17 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •