586,104 active members*
3,371 visitors online*
Page 9 of 10 78910
Results 161 to 180 of 183
  1. #161
    Re: New UC300ETH breakout board.
    You need to explain EXACTLY what you want to do. I think that FA/FB is a relay output? There's a parameter to set it to one of ±20 functions.
  2. #162
    Oct 2016
    66
    I wired my UB1 similarly as shown in the diagram attached. When the eStop is pressed, the relay is de-energized and cuts 24v power to the Nema drivers and also cuts the x103 circuit which triggers the software estop.
    I do not know how to use the same estop to turn off the vfd. I only mentioned FA & FB from an older post where someone used it for estop but did not specified how.
  3. #163
    Jul 2017
    Seeking recommendations on how and where to connect a simple E-Stop N.C. switch on the ETH300-UB1 without using a contactor or relay
  4. #164
    X103-X115(any one) to 0V.
  5. #165
    Jul 2017
    Thanks I did that and also selected pin3 on port 1... went low and high....no success...I'll double check continuity through out
  6. #166
    Nov 2006
    61
    Quote Originally Posted by Rybat57 View Post
    You can connect N.C switch across X103 and 0V.
    In the software configuration, setting the Estop signal to i102 ( port1, pin2).
    Later on, you can add any fault signal (Normally Close contact) to X104-110 and activate safety function for each input by soldering solder jumper at the bottom of the UB1 board.
    On the diagnostics page of UCCNC, you can see LED status while you toggling the switch.
    Weerasak.
    www.CNCRoom.com
  7. #167
    Aug 2016
    37
    Hello. Recently purchased the UB1 and long time UC300ETH/UCCNC user. I can't seem to find out any info on the switching frequency of the isolated inputs on the UB1 and don't see any non-isolated inputs? Would it be better to use one of the port outputs and use non-isolated input board for an encoder inputs? My encoder input is for the spindle, which can run up to 10k RPM, so worried about saturation of the input opto-couplers on the isolated inputs. So trying to determine if I should just get an add-on board to begin with for the spindle encoder input.
    Thanks for any information.
  8. #168
    Email CNC Room, he's very helpful.
  9. #169
    Aug 2016
    37
    Thanks Gerry. I didn't know contacting CNC room would go to the person making the UB1. Message sent. Will post back here any info just in case someone else is interested.
  10. #170
    Yes, Weerasak makes the boards and answers all the emails.
  11. #171
    Nov 2006
    61
    I used to measure some inputs waveform of UB1 and posted in CNCdrive forum.
    forum.cncdrive.com • View topic - adjustable debounce settings - suggestion
    The falling time is 7.6 micro second. However, fully one pulse will consist of falling time + settle time + rising time + settle time. From the above information, I wound probably multiple by 10 times for the worst case. Then, I simply convert to RPM by using an online calculator. the final result is 789,473 rpm.
    https://www.sensorsone.com/period-to...cy-calculator/
    On the similar input circuit of MB3, the software Mach4 able to read index input up to 862,200 rpm.
    However, In a few days I will check from the real UB1 and UCCNC again.
    Weerasak.
    www.CNCRoom.com
  12. #172
    Aug 2016
    37
    Quote Originally Posted by vrasak View Post
    The falling time is 7.6 micro second. However, fully one pluse will consist of falling time + settle time + rising time + settle time. From above infomation, I wound probably multiple by 10 time for the worst case. Then, I simply convert to rmp by using online calculator. the final result is 789,473 rpm.
    On the similar input circuit of MB3, the software Mach4 able to read index input at 862,200 rpm.
    However, I will check from the real hardware and software for you in few days.
    Thanks, but forgot to mention I'm using a quadrature encoder for spindle PID and rigid tapping. So the PPR will be much higher on the A/B channels. Currently the C11G board I'm using has 4MHz opto-isolators which allows me to use 200 PPR (set in UCCNC at 400 as it reads rising and falling edges) and I can still register 10k RPM. Any higher and it saturates the board.
    I thought you may have an actual frequency spec for the opto-isolator chips you used on the UB1 board so I could calculate out my max PPR. I'm using CUI AMT-102V encoders with adjustable resolution.
    Based on your calculated example above, it looks like you have roughly 13.3KHZ opto-isolators which will be too slow for me to use for the PID feedback in UCCNC.
  13. #173
    Nov 2006
    61
    Today I had a chance to hook things up and made a measurement waveform right on UC300 pins. The bad news is that the original UB1 V1.6 will catch endcoder signal at the maximum at 4.95khz due to conservative pull up resisters on certain pins. The picture below shows distortion of waveform.
    Weerasak.
    www.CNCRoom.com
  14. #174
    Nov 2006
    61
    Continue from the previous post.
    After changing the pull-up resistor from 4.7K to 1K. the waveform looks much better. However, this modification can achieve target only 13.66 Khz
    The below waveform is still in good shape. However, if we increase frequency higher than this, the position count is not correct. I haven't had a chance to check the maximum frequency that UC300ETH able to catch.
    The locations of the pull-up resistors need to be changed.
    Weerasak.
    www.CNCRoom.com
  15. #175
    Nov 2006
    61
    Since all hardware are already on the work bench. So, I take a chance to measure UC300ETH encoder input. This time I wire up quadrature signal from the ESS/MB3 to UC300ETH directly. This way UC300ETH gets proper waveform.
    From this experiment shows that UC300ETH able to catch quadrature encoder frequency at about 20 khz. The encoder position is starting inaccurate if go beyond than this.
    Weerasak.
    www.CNCRoom.com
  16. #176
    Aug 2016
    37
    Thanks VRASAK, I appreciate the information. For some reason, I never got any notification of this last reply, but just decided to check today.
    Anyway, based on your very first post, it was apparent the UB1 isn't designed for a quadrature encoder. To me, this would be a good addition to the board since UCCNC requires a quadrature for PID spindle control and rigid tapping. You would just need 2 high speed inputs (or just straight logic inputs with no isolation) for the A/B channels. But I guess for now, I'll just have to break out one of the pin headers for my encoder. Shouldn't be that big of a deal.
    Thanks for the information. Now I just need to get this UB1 incorporated into my new control system with all the new DMM servos and servo spindle drive.
  17. #177
    Aug 2016
    37
    So I'm thinking about just using this to breakout the port 4 or 5 IDC header for my encoder. You think it should be OK for this purpose?
  18. #178
    Nov 2006
    61
    You can connect the AMT encoder signal directly to the LPT4 and LPT5 as shown in the schematic below. This connection, the encoder will be part of the controller circuit. So, shield cable may be needed and it must be connected to the motor frame because we don't want to bring the picked up noise back to controller.
    Weerasak.
    www.CNCRoom.com
  19. #179
    Aug 2016
    37
    Thanks. Will do the shielded wire for sure. But for a few bucks, it's nice to have terminals to connect and I have plenty IDC26 cable laying around. LOL, i knew keeping those old computer stuff would come in handy one day.
  20. #180
    Aug 2016
    37
    So I haven't had a chance to test this out yet (as I'm still getting my new electrical enclosure together, but what frequency can the pass through ports handle (ports 4 or 5)?
Page 9 of 10 78910
  1. Replies: 25
    Last Post: 12-13-2016, 08:44 PM
  2. Help deciding which breakout board or driver board etc to use!
    By localbroadcast in forum Servo Motors / Drives
    Last Post: 06-09-2016, 09:25 PM
  3. BREAKOUT BOARD INTERFACE BUFFER BOARD
    By deslee in forum Servo Motors / Drives
    Last Post: 08-17-2014, 07:32 PM
  4. Breakout Board!!!???
    By Knucks in forum Stepper Motors / Drives
    Last Post: 03-25-2013, 10:12 AM
  5. Breakout board, Relays on board?
    By Cooper in forum Open Source Controller Boards
    Last Post: 06-10-2007, 01:55 AM
