The wire insulation shows no sign of damage so I am hopeful. My unit will only see occasional use. Monthly rather than daily.
Yes I understand that but for testing it is the max frequency which sets the V/f ratio and that is what caused my problems. Anyway that is done and finished with now.
However, you seem to be the guru here on these VFDs and I have some questions which I hope you can help with.
For 15 years or so I have been using an ABB VFD to drive a mill motor. That VFD is rated at 2.2 kW (the largest 1 to 3 ph VFD that I could find at the time) and originally it drove a 1 hp motor. i changed the motor to 5 hp and occasionally I inadvertently loaded it beyond 2.2 kW and it tripped out as expected. I have very recently got a 4 kW
Huanyang device to replace it to run the mill up to 60 Hz and also the 400 Hz spindle that I mentioned. So from time to time I will need to change the settings between the two. The old ABB unit had a macro feature in which I could save various parameter sets. Do you know if this is possible with the Huanyang unit? As others have mentioned the manual is somewhat lacking in explanation, but it shows settings for multiple frequencies without explanation. Are these available for some sort of similar macro feature for rapid change of driven motor? Otherwise it will be tiresome changing numerous parameters each time I change motors.