586,119 active members*
3,547 visitors online*
IndustryArena Forum > CNC Electronics > Spindles / VFD > 110v VFD's. Any issues?
Page 3 of 6 12345
Results 41 to 60 of 106
  1. #41
    Sep 2005
    1740
    Re: 110v VFD's. Any issues?
    I had a Chinese built 6040 router that came supplied to run on 120 volts with a 120 volt VFD. It ran great, no issues but I was not going to cut 3/4 inch plywood with one pass ether.
  2. #42
    May 2016
    34
    Question Re: 110v VFD's. Any issues?
    On 120V supply you have to have a minimum of 20A to run a 1.5Kw Spindle 25A would be better, so your normal 120v outlet is only 15A so you are not going to successfully run even a 1.5Kw Spindle on it so a 800w is about where you are at with only a 120v 15A supply
    Thanks mactec54, appreciate the help!
    All things being equal, if I ran a 20 amp line would the 1.5Kw spindle run better than a 800 watt on a 15 amp line?
  3. #43
    Sep 2005
    1740
    Most modern homes wired to Code the outlets are wired for 20 amps, check your circuit breaker panel for more information. Frankly I do not know what a 1.5 Kw spindle on 120 volts would draw. I know my 2.2 Kw VFD calls for a 30 amp breaker on 240 volts single phase. The larger spindles are not practical on 120 vac.
  4. #44
    15362
    Quote Originally Posted by AngelArs View Post
    Yes it would be better than 800W, if your are going to run a new line do it for 25A
    Mactec54
  5. #45
    May 2016
    34
    Is 8 gauge wire with a 30 amp wall outlet, and a 25 Amp circuit breaker correct? It's going around 30 - 40 feet max.
  6. #46
    15362
    10 Gauge is rated 30A
    Mactec54
  7. #47
    May 2016
    34
    Thanks mactec54. I thought 10 gauge was good up to 25 feet, but apparently not. Thank you for the correction.
    What style of 30 amp receptacle is best to use with something like this?
  8. #48
    15362
    You won't be using 30A on a 120v supply with a 25A Breaker you most likely won't go much of the 20A If you have changed your mind and are running a 240v circuit then I would go with the 8 Gauge 2 Hot Neutral and Ground that way you can have a 120v circuit and a 240V circuit from the same supply
    These are the best type of Plugs for these type of connections, if you are going to a cabinet the you need a disconnect at the cabinet
    This can be a 4 wire to your cabinet and then you can have 120v and 240v for your cabinet supply
    You would need a 4 prong Plug if you use a 4 wire supply
    Attached Thumbnails Attached Thumbnails 4 wire Twistlock Plug 30A.PNG   Twistlock Receptacle 30 Amp.PNG
    Mactec54
  9. #49
    May 2016
    34
    Thanks again mactec54, appreciate all the help! Trying to do all my research before I buy anything.
    I haven't changed my mind. I'll be running 10/3 Romex to the VFD, and then 16/4 double
    shielded from the VFD to the 1.5kw spindle.
  10. #50
    15362
    Romex is not normally used unless this is a permanent installation this is ok for in the wall to a outlet, but not for a cable from the wall outlet to cabinet
    Mactec54
  11. #51
    May 2016
    34
    Yes this will be permanent in wall install with cable run inside conduit.
    I'll then use a cable like you see used on a stove and use that to connect from the wall outlet to the VFD.
  12. #52
    15362
    The Shielded Cable from the VFD to the Spindle does not have to be 16 Gauge but that will work
    CF6-15-04 is a IGUS cable which is as good as it gets this is 16 Gauge 18A Rating
    CF6-10-04 is 17 Gauge with a 15A Rating
    CF6-07-04 is 18 Gauge with a 12A Rating
    Mactec54
  13. #53
    15362
    Ok one problem you can not Plug and Unplug a VFD Drive without first turning the power off with a Quality Disconnect switch you need a Switch and a EMI Power Filter between the Power supply and the VFD Drive
    Mactec54
  14. #54
    May 2016
    34
    Lightbulb Re: 110v VFD's. Any issues?
    I was going to use a disconnect switch next to the outlet, possibly this one;
    https://www.amazon.com/gp/product/B0...A3VRYS8E&psc=1
    or this one;
    https://www.amazon.com/Woodstock-D41...QTNWHK6GDYPMV8
    I am am looking into using a UPS to filter the power, as well as building a positive pressure filtered enclosure for the VFD.
  15. #55
    15362
    or this one;
    No you would not want to use a UPS for a VFD Drive supply, the Filter I posted is what should be used , if your outlet has a box big enough you could put the Filter in that box or if you have a machine cabinet that is the best place for the Filter and closer to the VFD Drive
    Yes they would work which one would depend on what you are mounting on the wall Ideal a disconnect is like the snip below and is mounted at the control cabinet, there are many types of disconnect switches that could be used
    Mactec54
  16. #56
    May 2016
    34
    According to Lincoln Electrics EMI manual a properly sized UPS is fine. I will post a link to their manual tonight when I get home from work.
    Do you have a link to the EMI filter that you posted?
  17. #57
    15362
    Here is one of many suppliers https://www.digikey.com/product-deta...30L-ND/2136855
    Most are using this Filter or one similar
    Mactec54
  18. #58
    May 2016
    34
    Here's the link;
    Concepts of Signal Noise Reduction - Shielding and Grounding
    The entire manual is a good read. See page 22;
    Whether I use the UPS or not I will still use the one you posted a link to.
    It installs right before the disconnect and receptacle correct?
  19. #59
    15362
    Here's the link;
    This has nothing to do with being used inline with a VFD Drive which I would not attempt to do
    Mactec54
  20. #60
    May 2016
    34
    Why? Is that because the amperage is too high for a UPS?
Page 3 of 6 12345
  1. VFD Huajiang YL600-2s-1K5 G 110v
    By mrbigde in forum Spindles / VFD
    Last Post: 12-19-2017, 04:29 AM
  2. 110v 2.2kw VFD/spindle help
    By factory5150 in forum Spindles / VFD
    Last Post: 08-10-2017, 01:16 AM
  3. 62mm 110V Spindle
    By Bob La Londe in forum Want To Buy...Need help!
    Last Post: 06-08-2016, 07:03 PM
  4. Spindle motor and VFD for 110v
    By shadowless in forum CNC Machine Related Electronics
    Last Post: 03-26-2009, 04:51 AM
  5. 110V power in
    By krymis in forum CNC Machine Related Electronics
    Last Post: 04-16-2008, 05:12 PM