I use a 2.2Kw water cooled Chinese spindle.
I actually used your list for parameters last time I set the parameters.
PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
PD001=0 (1 For Remote Control)
PD002=0
PD003=400
PD004=400
PD005=400
PD007=20
PD008=220
PD011=120 (Minimum Setting 120) This can be set at 100 But 120 is a safer number to use with this VFD
PD009=15
PD010=8
PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
PD014 Accel=12 ( Adjust to suit)
PD015 Deccl=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
PD141=220 ( Motor Rated Voltage )
PD142=9 ( Motor Max Amps) (Set for your motor Amp Rating 2.2Kw Spindle 9 amp Max)
(Set for your motor Amp Rating 1.5Kw Spindle 7 amp Max)
PD143=2 ( Motor Number of Poles)
PD144=3000 (Max Motor RPM) =3,000= (24,000)
The only difference is that I use remote controlled start and stopp PD001=1 but not remote controlled speed control PD002=0 due to inconsistent speed.
Since I have messed around with the settings before it could be some other parameters I have set without remembering other places. I can try to do a factory reset and only set the parameters in the list and se if it changes anything.
Edit:
Just tried turning off the remote control for the start and stop signal for the VFD. Afterwards I manage to do a long run without any stops. Ill do some more testing and see if the problem re appears.