    Help with Timer Relay

    I have a Wieland KZT 510 K and am having problems trying to decipher the wiring diagram. Can anyone with schematic experience help??

    Attachment 400448

  2. #2
    Join Date
    Dec 2013
    Posts
    5717

    Re: Help with Timer Relay

    Power goes to L1 - N, in this case 24V AC or DC, in the case of DC L1 is +. A1 and A2 is the input power to the unit. B1 is the start timing signal, also connected to L1 through a switch. 15 is Common, 16 is NC, 18 is NO
    Jim Dawson
    Sandy, Oregon, USA

  3. #3

    Re: Help with Timer Relay

    Thank you Jim!

  4. #4

    Re: Help with Timer Relay

    Jim, on this Wieland unit, there are 4 dials, a pair each for delay on and delay off I would guess.

    I'm planning on using this as a delay off to control a 220v fan, letting it run for 5 minutes after the spindle is shut down.

    Do you know which set I would use? One dial is timing and the other is graduated from .1 to 1. What is that used for??

    You also mentioned that B1 was the start timing signal. Could that be an output signal from the VFD?


    Attachment 400466

  5. #5
    Join Date
    Dec 2013
    Posts
    5717

    Re: Help with Timer Relay

    I'm not sure which is OFF delay and which is ON delay. Just play with it a bit and you'll be able to see how it all works. I think the 10ths dials are a percentage of the base setting, so if you set for 1 second and 0.1 it would time for 0.1 second. Same for minute and so on.

    You should be able to use the relay in the VFD to trigger the timer any way you want.
    Jim Dawson
    Sandy, Oregon, USA

  6. #6
    Join Date
    Nov 2012
    Posts
    1267

    Re: Help with Timer Relay

    The two dials are for fine and coarse time settings.
    For instance, if you want a 60-second delay, you set the first dial to "100s" and the second dial to "0.6". 100*0.6=60 seconds.

  7. #7

    Re: Help with Timer Relay

    In case anyone ever stumbles upon this thread, here is what I did to get this relay timer integrated into my control cabinet.

    As Jim stated above:

    A1 - +24v DC
    A2 - -24V DC
    B1 - signal from VFD (+24v DC)

    15 - Common (240v AC)
    18 - To spindle fan

    Top set of dials is for 'on delay' and the bottom set for 'off delay'. And as Jim and CitizenOfDreams indicated they are course and fine setting.

    Thanks for your help gentlemen!

  8. #8
    Join Date
    Dec 2013
    Posts
    5717

    Re: Help with Timer Relay

    My pleasure to help out :cheers:
    Jim Dawson
    Sandy, Oregon, USA

Similar Threads

  1. Replies: 12
    Last Post: 01-30-2023, 01:23 PM
  2. Is a timer relay what I need???
    By bobmagnuson in forum CNC Machine Related Electronics
    Replies: 2
    Last Post: 08-08-2018, 02:23 PM
  3. Relay timer for solenoid.
    By moto52000 in forum CNC Machine Related Electronics
    Replies: 17
    Last Post: 12-04-2011, 06:54 AM
  4. Using a solid state relay as a main stop relay
    By garagefela in forum CNC Machine Related Electronics
    Replies: 4
    Last Post: 02-26-2010, 11:27 PM
  5. Electronic relay Timer Question
    By Chris64 in forum Uncategorised MetalWorking Machines
    Replies: 15
    Last Post: 01-18-2009, 04:56 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •