Re: Switch for Rapid Turn.
Originally Posted by
jttoner
Back to the switch in question would a 220 VAC 15 Amp switch be able to handle the load. The VFD would be shut down during switching operations.
Yes, a 15A rated 3 phase switch will be plenty for the 1.5hp Tormach motor (each phase carries about 7A at full load).
You are not the first to do this; there is at least one other person on this forum that installed a 3 phase switch. There also used to be a product on ebay which was a switched USB socket, which would allow you to easily reprogram your VFD when making the switch from mill to RT.
Tim