Hey Guys, back to my boss .. typical 2 hp motor .. what's my best choice for VFD
thanks !
Joe
Hey Guys, back to my boss .. typical 2 hp motor .. what's my best choice for VFD
thanks !
Joe
Mactec54
thanks Mac,
this is the drive i ended up ordering
10.5 FLA and includes braking transistor
https://www.factorymation.com/TD400-2003-13PH
the bigger ones were all 3 phase input so hope it works !!!
Joe
3 phase input has nothing to do with it, a 3 Phase input VFD Drive still runs on Single Phase don't believe what a sales person tells you
A 3hp that you got should do the job with having the braking resistor, the Rated Input Amps that the Drive can use is what is important when using Single Phase supply that needs to be a minimum of 10A for your motor so that is 10Amps on the input not the output of the VFD Drive if it can't do that then send it back and get one that can
Mactec54
Mac, thanks for the input.. i have reached out to this company to find out the input amps... The rated output current (A) is 10.5 and the rated input current (A) is 23.9 / 12.5 depending upon if you are using single or three phase.