Hi Folks,
I've tried the usual reset protocols after the Battery is replaced.
Done the Keeper Relay #5.0 to 1 and all.
I've done the routine a dozen times pressing even a few times with the three button holding portions.
It will set all the PMC values that I've seen to Tool 1 and looks to be all set.
Even done power off and back on to see if there was a need for it.
Here's where it goes wonky!
If I don't move the turret to a new position and attempt to set tool 1 using the "Qsetter" it will open the table to tool 1.
If I rotate the turret to position 2 (or anywhere else) it sends the table to Tool 16 and no matter where the turret is it opens the table to tool 16 forever after.
If I try to program the turret move in MDI or Prog Mode, the turret indexes and clamps but never moves to the next line.
I did check the switches to be sure the clamp and unclamp switches swap 0's and 1's during a manual move. It is clamping! but the line never finishes...never!
I have been at this too long to get this far and not succeed... but folks this one is weird.
I have even taken the new battery out and brought up the original alarm...hoping to start from scratch and no different result.
This is only a 12 tool position turret!