    Size for ground wires

    Hi,

    at the moment I'm building the control panel and could need a little help with the size of the ground wires.


    The source wire is 1,5mm^2. All consumers are internal connected to a star point. Would it be a problem if the consumers ground wires to the star point are thicker (2,5mm^2) than the input source ground wire or is it necessary that the wires to the star point are smaller than the source wire?


    Here are some pictures: (In the future all ground wires will go to ground temrinal blocks on a rail..)

  2. #2
    Join Date
    Jan 2005
    Posts
    107

    Re: Size for ground wires

    Never smaller .Larger ok.

  3. #3
    Join Date
    Mar 2018
    Posts
    70

    Re: Size for ground wires

    Ok. Thanks. Another question:

    As you can see on the picture the panel has three line-in wires. Each one with hot/neutral/ground.


    I would like to crimp their grounds together and use them like one large ground wire. Is this a problem?

  4. #4
    Join Date
    Jan 2005
    Posts
    15362

    Re: Size for ground wires

    Quote Originally Posted by millhouse_ View Post
    Ok. Thanks. Another question:

    As you can see on the picture the panel has three line-in wires. Each one with hot/neutral/ground.


    I would like to crimp their grounds together and use them like one large ground wire. Is this a problem?
    That is not a good Idea, how can you have 3 Main Power Supplies from 3 different power outlets, you should only have ( 1 ) for your whole cabinet
    Mactec54

  5. #5
    Join Date
    Dec 2003
    Posts
    24221

    Re: Size for ground wires

    Quote Originally Posted by millhouse_ View Post
    Ok. Thanks. Another question:

    As you can see on the picture the panel has three line-in wires. Each one with hot/neutral/ground.


    I would like to crimp their grounds together and use them like one large ground wire. Is this a problem?
    One example is DIN rail mount terminals, you can get them with automatic ground to the enclosure, they are half green, half yellow, and are intended for such cables that also include a ground conductor.
    The ground in this instance is through enclosure bonding, but also pays to take a single correctly sized one to the star point also.
    This is the method I have used for over 50yrs.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  6. #6
    Join Date
    Mar 2017
    Posts
    411

    Re: Size for ground wires

    Quote Originally Posted by millhouse_ View Post
    Ok. Thanks. Another question:

    As you can see on the picture the panel has three line-in wires. Each one with hot/neutral/ground.


    I would like to crimp their grounds together and use them like one large ground wire. Is this a problem?

    What you want to do is try not to create a ground loop. If you connect all the grounds together from the three sources you have created 3 loops. Most likely the 3 ground wires from the power panel are all connected together in the panel. So, only a single wire is needed for your ground. It should be a large enough gauge to carry the load of the 3 lines combined.

    The purpose of the ground wire is to provide any stray energy in your device the path of least resistance to ground. If there was no ground connection then a short of a main wire could cause the cabinet to be at a high potential. When you touch the cabinet, then you become the shortest path to ground (this is bad).

  7. #7
    Join Date
    Dec 2003
    Posts
    24221

    Re: Size for ground wires

    The Ground wire should be the same gauge as the supply conductor or same as the combined size, if supply is from difference sources.
    All ground wires should terminate at the star point or be joined and continued with a single conductor equal to the combined gauges.
    The service ground should also terminate at the Star Point GND.
    There was a copy of NFPA79 out there if needing guidance on regs for enclosure wiring.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  8. #8
    Join Date
    Jan 2005
    Posts
    15362

    Re: Size for ground wires

    Quote Originally Posted by millhouse_ View Post
    Hi,

    at the moment I'm building the control panel and could need a little help with the size of the ground wires.


    The source wire is 1,5mm^2. All consumers are internal connected to a star point. Would it be a problem if the consumers ground wires to the star point are thicker (2,5mm^2) than the input source ground wire or is it necessary that the wires to the star point are smaller than the source wire?


    Here are some pictures: (In the future all ground wires will go to ground temrinal blocks on a rail..)
    This is a good question, so if other devices require or have a larger Ground wire, this could indicate that your main supply is to small 1.5mm is only 15 Gauge ( close enough to 16 Gauge ) most cabinet's need at least a 30A supply which would be 10 Gauge, so I would say you input supply is a little on the light side

    What size is the VFD Drive ??? this will need a Power Filter on it input supply

    The Mains Power Supply Ground Connects at the Star Point
    Mactec54

  9. #9
    Join Date
    Mar 2018
    Posts
    70

    Re: Size for ground wires

    Thanks for the feedback.


    The first power input is for the 5v and 12v power supplies and maybe for other stuff in the future like a vacuum cleaner etc. And it is connected to a contactor that switches on the other two inputs ( one for the steppers and one for the spindle ). Normally I would have used 3-phase current for this but I don't have the possibilities for this.

    @mactec54

    The consumers don't need 2,5mm^2. I just used it for them.

  10. #10
    Join Date
    Jan 2005
    Posts
    15362

    Re: Size for ground wires

    Quote Originally Posted by millhouse_ View Post
    Thanks for the feedback.


    The first power input is for the 5v and 12v power supplies and maybe for other stuff in the future like a vacuum cleaner etc. And it is connected to a contactor that switches on the other two inputs ( one for the steppers and one for the spindle ). Normally I would have used 3-phase current for this but I don't have the possibilities for this.

    @mactec54

    The consumers don't need 2,5mm^2. I just used it for them.
    Ok what size is the Spindle Motor and VFD Drive how many Kw and Amps
    Mactec54

  11. #11
    Join Date
    Sep 2005
    Posts
    1740

    Re: Size for ground wires

    We routinely build control panels for production lines with multiple power sources and grounds. They are all sourced from the building main 13.8 Kv and substations. All grounds are tied back to the main substation. It makes no difference. Your control panel needs a disconnect for each source.
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

  12. #12
    Join Date
    Jan 2005
    Posts
    15362

    Re: Size for ground wires

    Quote Originally Posted by wmgeorge View Post
    We routinely build control panels for production lines with multiple power sources and grounds. They are all sourced from the building main 13.8 Kv and substations. All grounds are tied back to the main substation. It makes no difference. Your control panel needs a disconnect for each source.
    "Routinely build control panels" the last control box you used I recall you brought it already made for your hobby machine
    Mactec54

  13. #13
    Join Date
    Sep 2005
    Posts
    1740

    Re: Size for ground wires

    Quote Originally Posted by mactec54 View Post
    "Routinely build control panels" the last control box you used I recall you brought it already made for your hobby machine
    Before I retired and started drawing the bucks for not working… just being a hobby guy. Yes even my hobby panels are wired to Code. We wired some pretty good sized industrial plants.

    Looks like Al and I did the same work.
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

  14. #14
    Join Date
    Dec 2003
    Posts
    24221

    Re: Size for ground wires

    Quote Originally Posted by wmgeorge View Post

    Looks like Al and I did the same work.
    Could be.
    Mostly retro fits, PLC control panels and CNC retro fits with Fanuc and Mitsubishi, designed a few custom ones with Galil motion cards, which are a pleasure to use.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  15. #15
    Join Date
    Sep 2005
    Posts
    1740

    Re: Size for ground wires

    Quote Originally Posted by Al_The_Man View Post
    Could be.
    Mostly retro fits, PLC control panels and CNC retro fits with Fanuc and Mitsubishi, designed a few custom ones with Galil motion cards, which are a pleasure to use.
    Al.
    Not the same. I installed and wired production lines, moved old junk machines at times into the modern world. Plus new stuff also, some PLCs. some solid state control systems as prototypes and just a lot of MCC wiring to machines and tying in interlocks and the like. At the time I was working under a very strict Master Electrician. Later on I was the sole electrician for second shift production. Loved every minute of my electrical work. Later got into Commercial HVAC/R work specialized in controls.
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

  16. #16
    Join Date
    Mar 2018
    Posts
    70

    Re: Size for ground wires

    This is it now:





    Attached Thumbnails Attached Thumbnails 2222.jpg   3333.jpg   5555.jpg  

  17. #17
    Join Date
    Dec 2003
    Posts
    24221

    Re: Size for ground wires

    Quote Originally Posted by millhouse_ View Post
    This is it now:
    I see you are already using the DIN rail GND terminals!
    Some cable trough would have neaten'd it up a little!
    Max.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  18. #18
    Join Date
    Jun 2010
    Posts
    4256

    Re: Size for ground wires

    Not mentioned yet is the function of a Ground wire - why have one? There are two reasons, and really two different sorts of ground wires.

    The first is safety. If something exciting goes wrong, you want the Ground wire to be able to handle as much current as the Active can supply which might be 30 - 40 A. This is why you often see instructions that the ground wire should never be smaller. Note this well.

    The second reason for a 'Ground' wire is to serve as a screen, to block EMI or radiated interference. For instance, you should Earth the screen around your spindle PS cable. In general, the Ground wire from such a screen does not need to carry 30 A. Within reasonable limits of distance, quite light electronics hookup or signal wire is adequate for the screening. I won't go into the fact that high-frequency interference usually sits on the exterior of a copper conductor anyhow.

    The tricky bit can be when there is a risk of a Mains fault to a low-voltage power supply lead. This is a bit of a cross-over case. In practice, we usually use slightly more than 'light electronics hook-up wire' for this.

    My 2c.
    Cheers
    Roger

  19. #19
    Join Date
    Sep 2005
    Posts
    1740

    Re: Size for ground wires

    The equipment grounding wire is required by electrical code for safety, and sized to the main power input source, the EMI drain is a bonus. Yes your shields should be grounded to this ground as your metal cabinets are also.

    To clear up confusion, the DC and signal power negative
    ( - ) should not be tied to equipment ground unless instructed (?) as its not the same thing as it carries voltage.
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

  20. #20
    Join Date
    Dec 2003
    Posts
    24221

    Re: Size for ground wires

    Quote Originally Posted by wmgeorge View Post
    To clear up confusion, the DC and signal power negative
    ( - ) should not be tied to equipment ground unless instructed (?) as its not the same thing as it carries voltage.
    Yeah, there is two thoughts on this, some practice never grounding the power commons of different sections of equipment, IOW keep all power separate, and the opposing view on grounding at all times if it is possible.
    I have always prescribed to the latter, whether the equipment supplier has decreed it or not.
    I know of a few instances here in the past where posters have had 'noise' issues caused by false triggering of inputs due to injection of noise which can be inductive or capacitively coupled. Such problems were cured after grounding all power common.
    There is also a practice that was outlined in a Siemens paper covering the importance of something called equi-potential bonding, this ensures that all metallic parts of a machine are at the same ground potential, this practice virtually eliminates the occurrence of Ground Loops.
    The above has so far kept me in good stead!
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Page 1 of 2 12

Similar Threads

  1. Stepper motor wires size, possible step loss?
    By QinX in forum Stepper Motors / Drives
    Replies: 15
    Last Post: 03-24-2017, 05:39 PM
  2. help with wires
    By linkintiger in forum DIY CNC Router Table Machines
    Replies: 15
    Last Post: 02-25-2011, 04:00 AM
  3. Frame ground vs. Electrical ground.
    By polaraligned in forum CNC (Mill / Lathe) Control Software (NC)
    Replies: 2
    Last Post: 11-24-2008, 11:21 PM
  4. To Ground or not to Ground That is the question!
    By Mr.Chips in forum DIY CNC Router Table Machines
    Replies: 1
    Last Post: 03-16-2008, 09:10 PM
  5. Motor supply ground vs Logic ground?
    By Gashmore in forum CNC Machine Related Electronics
    Replies: 11
    Last Post: 06-07-2005, 11:21 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •