Quote Originally Posted by justinwol View Post
@handlewanker HY02D223B Huangyang VFD (2.2KW 11A) with a 2.2KW water cooled spindle (24,000rpm).

@mactec54 The faults did not seem to affect the operation at all - it seemed to run fine. Here are the parameters I set after resetting the VFD:

PD001 = 0
PD002 = 1
PD003 = 120
PD004 = 400
PD005 = 400
PD006 = 2.5
PD007 = 0.5
PD008 = 220
PD009 = 15
PD010 = 8
PD011 = 100
PD014 = 12
PD015 = 12
PD070 = 1
PD072 = 400
PD073 = 100
PD141 = 220
PD142 = 9
PD143 = 2
PD144 = 3000

Seems to be working fine, temperature is cool both to touch and the water. No faults have shown up yet.

Thanks for the help guys. This is way I posted here, to get some feedback/criticism before I begin operating it regularly.
So as I said they where nothing to worry about as what is in the fault report has nothing to do with how it is running, they probably where from the factory testing and where never cleared, you have to be careful what you mess with

PD003=400 not 120 ( Main Frequency )

PD007=20

PD014= is adjustable normally can get them down to around 3s to 6s without a fault

PD015= is adjustable the same as well

PD174= ??? ( To Be Set to the VFD Drives Max Rated Output Amps )

The temperature on the outside is not an indication of the temperature on the inside the water does a good job most of the time though, have the water run longer when the spindle turns off

Do you have the Ground wire 4th Pin in the spindle connected this is a must to check that it is Grounded to the body of the spindle