Hi
I have a Huanyang VFD HY01D511B 110V 1.5kw, and when I turn it on, the potentiometer display turns on as usual and when I press the run key,
the spindle start until it reach the maximum speed, without turning the speed knob of the potentiometer wich remain at zero. (seems disable).
I had previously program VFD PD.... according to instructions obtained from Mactec54 post
"This is all you need, all the basic Parameter Settings are the same for all the 400Hz Spindles, just voltage and Amps that are different
Don't do a Reset unless you have to, sometimes doing this affects the order of how the Parameters get set
" Huanyang Mactec54
PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
PD001=0 (1 For Remote Control)
PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )
( J1 Also Needs to be set for Terminal Control )
PD003=400
PD004=400
PD005=400
PD007=20
PD008=220 (120 If you have 120v VFD )
PD009=15
PD010=8
PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)
PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
PD014 Acceleration=12 ( Adjust to suit)
PD015 Deceleration=12 (Adjust to suit)
( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )
PD142= ( Motor Max Amps)
PD142=( 220vSet for your motor Amp Rating 2.2Kw Spindle 9 amp )
PD142=( 220VSet for your motor Amp Rating 1.5Kw Spindle 7 amp )
PD142=( 220v Set for your motor Amps Rating 800w Spindle 4 amps )
PD142=( 120v Set for your motor Amp Rating 800w Spindle 7 amp )
PD143=2 ( Motor Number of Poles)
PD144=3000 (Max Motor RPM) =3,000= (24,000)
PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )
PD72=400
PD73=120 ( 100 Minimum Setting )"
Does anyone have an idea of the problem ? Should I do something with the J1 jumper ?
Thank you
Jack