Hello everyone!
Wondering if some could tell me if I would have any trouble using my 2.2KW VFD with a 1.5KW Spindle.
Cheers,
Bran
Hello everyone!
Wondering if some could tell me if I would have any trouble using my 2.2KW VFD with a 1.5KW Spindle.
Cheers,
Bran
Thanks a lot! So do i just lower the amps on the VFD to 6 amp ? 6 x 220V = 1320 watt
No you have to use the motor spec's, so the Parameters would be set to suit the spindle motor spec's and this is important or you will damage the VFD Drive or the spindle, this can happen no matter what the VFD Drive size is incorrect Parameter settings are the cause of most failures
Mactec54
How does one learn about that ? these are the specs for the spindle
Power: 1.5 KW,
Voltage: 220V~250V,
Frequency: 400 Hz
I know how to set the max hz to 400 on the VFD and its a 220V VFD. Im assuming i have to lower the amps but i am new to all this
Hello.
I agree with mactec54, a misconfigured drive is a good source of problems.
I also think you should check for the fuses and/or thermal breakers and have them selected accordingly. They are your last line of defense should a problem arise.
As the drive is capable to deliver higher current than your motor requires imagine a situation where the motor gets stalled. The only way for the drive to know is by the current increase. Yet if misconfigured it may try to deliver it effectively burning the motor and probably itself.
Note: the previous assumption may not be correct if there is some sort of feedback from the motor to the drive. However I always prefer to be safe than sorry.
I hope this helps.
Regards.
The VFD is a Hy Series HY02D223B https://bulkman3d.com/product/spk-2200/
The spindle hasn't arrived yet and i didn't have much of a choice in Australia, due to covid-19 no one has stock.
The write up says -
1.5kw
400hz
220V~250V
8000-24000 R/min
And assuming the picture is of the actual unit i can see printed on the spindle case "5 AMP"
Any help is greatly appreciated as i said im just learning about all this,
Thanks
Bran
Do you have the manual for the VFD drive if so how are the Parameters listed are the first part of the Parameter listed as PD_____ if so you have the real HY VFD Drive there are a lot of copies that is why I'm asking
The link is for a 2.2Kw the spindle you have ordered is a 1.5Kw water cooled or air cooled
Mactec54
Hey Mactec thanks for baring with me, yes the parameters begin with PD.
The spindle ive ordered is 1.5KW air cooled. The link was just to display the VFD i have, sorry for the confusion.
Basically the 2.2kw spindle that came with the VFD was way to heavy for my machine so i sold it and downgraded to a 1.5kw air cooled. I was unable to get a 1.5kw Huanyang, there just isn't any where with stock in Australia. But the specs for the one ive ordered are as quoted.
-Bran
This is what you need to start with for Parameter settings and input wiring, there may have to be some changes once you have it running
Huanyang Mactec54
I recommend that you use a EMI Power Filter this would be mounted close to the input Power connections of the VFD Drive Here is a good one to use
TDK Lambda RSEN2030L this is a EMI Rated Power Filter
Input Wiring R =Live/ Hot T Neutral in your case and Ground to the Ground Terminal
1.5Kw 400Hz 220v Water Cooled / Air Cooled
PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
PD001=0 (1 For Remote Control) ( 1 For 0-10v Terminal Control or Remote Trim Pot Control ) ( J1 Also Needs to be set for Terminal Control )
PD002=0
PD003=400
PD004=400
PD005=400
PD006=125
PD007=20
PD008=220 (Motor Rated Voltage)
PD009=69
PD010=11
PD011=150 ( 100 Minimum Setting with Quality VFD, 120 is Safe for Water Cooled )
(Air cooled 150 depending on Temperature this may be lower )
PD13= 08 ( Is for Factory reset, Only use this to set VFD to Factory Default Settings )
PD014=8 ( Acceleration Adjust to suit)
PD015=8 ( Deceleration Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
PD120=120 ( Stall Prevention )
PD141=220 ( Motor Rated Voltage )
PD041=8 ( Carrier Frequency max up to 10 )
PD142=6 ( Motor Max Amps for 1.5Kw Spindle)
PD143=2 ( Motor Number of Poles)
PD144=3000 (Max Motor RPM) =3,000= (24,000)
PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )
PD72=400
PD73=150 ( 100 /120 Minimum Setting Water Cooled AIR Cooled 150 )
PD120=120
PD174= (Set to Max VFD Drives Output Amp Rating )
PD006 and PD009 may need to be changed depending on the minimum Frequency Speed setting PD011 and PD73
Mactec54
Thank you so much for taking the time to help me with this
Hey Mac, just had a quick question. I did all your settings seems to be working, the only thing is i cant push past 275HZ. I read that i want to hit about 330hz for plywood so im wondering if something in your settings has capped the Hz cause my spindle shouldn't be pushed past 275 for safety
Thanks again man