586,072 active members*
4,746 visitors online*
IndustryArena Forum > CNC Electronics > Spindles / VFD > VFD HY 2.2kw 220v wiring to UB1 Controller Help
Page 1 of 2 12
Results 1 to 20 of 23
    Mar 2020
    60
    Lightbulb VFD HY 2.2kw 220v wiring to UB1 Controller Help
    Hello, all
    Need some help to setup VFD to UC300ETH-UB1.
    Read both manual for UB1 and VFD HY. not much on how to setup wiring.. Most of the information i got from reference on YouTube.
    On my diagram hive following wiring set, except the last wire (AH1), which im not sure where it go.
    On the VFD pin 1,2 are jump for external connection.
    From VFD DCM+FOR connected to UB1 on ON/CM1 relay
    The other configuration came up with:
    AL1---> VFD---> ACM
    AO1--> VFD---> AL
    AH1--> VFD---> not sure
    If anyone can help me connect this right way., So i don't end up doing damageto VFD or UB1.
    Appreciate all the help i can get...
    And to everyone be safe out there.
    Re: VFD HY 2.2kw 220v wiring to UB1 Controller Help
    UB1 --- VFD
    AH1 --- +10
    AO1 --- VI
    AL1 --- ACM
    Mar 2020
    60
    Thanks so much
    Mar 2020
    60
    Need help with the VFD Parameters.
    when i type M3 24000, spindel dosen't move, when i go back to jump VR spindle works fine...
    Jump on V1
    My parameters in VFD
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD008=220
    PD013=00
    PD044=1 to use FOR
    PD070=? SET FACTORY 0 <---?
    PD072=400
    PD141=220
    PD144=24000
    Screenshot of uccnc spidle setting..
    Try:
    S24000
    M3
    Mar 2020
    60
    didn't work
    Mar 2020
    60
    So i double checked the parameters my VFD HY 220 2.2kw
    My spindle is:
    GDZ-80-2 2B
    220V 2.2KW 8A
    400Hz 24000rpm
    VFD parametters
    PD000=0
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=.50
    PD008=220
    PD009=13.0
    PD010=6.5
    PD011=00.0
    PD013=00
    PD014=20.0
    PD015=20.0
    PD044=1
    PD070=
    PD072=400
    PD073=0.00
    PD141=220
    PD142=11.0
    PD144=3000
    On UCCNC spindle screen, What port is AL1,AO1,AH1 connected too?
    15362
    Quote Originally Posted by akihiko View Post
    My spindle is:
    GDZ-80-2 2B
    220V 2.2KW 8A
    400Hz 24000rpm
    VFD parametters
    PD000=0
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=.50
    PD008=220
    PD009=13.0
    PD010=6.5
    PD011=00.0
    PD013=00
    PD014=20.0
    PD015=20.0
    PD044=1
    PD070=
    PD072=400
    PD073=0.00
    PD141=220
    PD142=11.0
    PD144=3000
    Yes PD070=0 for 0-10v control ( 1 ) for Pot control
    PD011=100
    PD073=100
    Mactec54
    Mar 2020
    60
    thanks, after the two changes made in VFD parameters below
    PD011=100
    PD073=100
    key in M3 , but run at only 100 slow, make noises
    check video uploaded youtube:
    https://youtu.be/vI040tahPVc
    help.
    Port 4 pin 1, as shown on page 24 of the UB1 manual.
    Mar 2020
    60
    hey, ger21
    can you help get VFD up and running..
    VFD parametters
    PD000=0
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007= 20
    PD008=220
    PD009=15
    PD010=8
    PD011=120.0
    PD013=00
    PD014=12
    PD015=12
    PD044=1
    PD070=0
    PD072=400
    PD073=120.0
    PD141=220
    PD142=8.5
    PD144=3000
    when M3 spindle start, but run at 120,
    when type 2400 it run at 100.
    if over post, you see picture's /video/ wiring from VFD to UB1.
    im hiving a hard time it.
    thanks
    PD072=400
    PD073=120.0
    You have these backwards
    PD072 = 120
    PD073 = 400
    You also have it wired wrong.
    Move the wire from AI to VI.
    Measure the voltage between ACM and VI at different speeds. You should get 5V at 12000 rpm, and about 9.8V at 24000 rpm.
    If you don't, measure the voltage on the UB1 between AO1 and AL1. You should be seeing the same voltages.
    15362
    PD072 = 120
    PD073 = 400
    You are confused the Parameters are correct
    Mactec54
    15362
    PD011=100
    PD073=100
    help.
    Wiring is incorrect
    100Hz =6,000 RPM 120Hz = 7,200 RPM
    Mactec54
    The manual I have is wrong. It shows them both ways in different places. Sorry for the mistake.
    Mar 2020
    60
    Which wiring?
    Mar 2020
    60
    Wiring is incorrect
    Which wiring?
    the wiring from UB1 to VFD.
    AL1 ---> to VFD ---> ACM
    AO1 --> to VFD ---> AI
    AH1 --> to VFD ---> 10V
    or
    VFD and Spindle is working fine,
    When change PD001 & PD002 back to 0, Operator mode.
    The spindle run 0 to 400hz with no problem. i double check the wiring to spindle.
    VFD --> Spindle
    U --> pin 2
    V --> pin 1
    W --> pin 3
    G --> pin 4 is wire, but not use at this time.
    As I said before, move the wire from AI to VI.
    AI is for current, VI is for 0-10V
    15362
    Which wiring?
    or
    VFD --> Spindle
    U --> pin 2
    V --> pin 1
    W --> pin 3
    As Gerry has said VFD wiring is incorrect just one change VFD ---> VI and to check that you have 0-10v from the control when you make a speed change 5v = around 12000 Rpm so in MDI M3S12000 and check the voltage output before you run the spindle, yo must have the output voltage working before you connect to the spindle
    Normally the wiring for the spindle is
    Input wiring R T and Ground Terminals
    U=Pin 1
    V=Pin 2
    W=Pin 3
    Ground Pin 4
    Mactec54
    Mar 2020
    60
    U=Pin 1
    V=Pin 2
    W=Pin 3
    Ground Pin 4
    The output AH1 is 5v to 10v
    it working now.
    M3 run @ 12000 & S24000
    i check all my wiring all good.
    One question, about stepper driver and setting..
    Stepper Drive DM542A and the DIP switch setting
    sw1=on , sw2=on , sw3=off = Peak-> 2.84 / RMS->2.03
    sw4=off --> Half current
    sw5=off , sw6=off , sw7=on , sw8=on -->1600
    Stepper motor:
    57HD6401-14S 1.8` 3A N1905
    The reason im asking is because my AXIS sound a little rough. X, Y, Z,
    A picture of UB1 AXIS setting..
    maybe i need turn them?
    thanks for all the help on the VFD & Spindle guys
Page 1 of 2 12
  1. 220v vfd wiring
    By Chmexdf5633 in forum Spindles / VFD
    Last Post: 03-16-2020, 09:44 PM
  2. Wiring 3P 380v or 1P 220v
    By jwilcott in forum Chinese Machines
    Last Post: 11-18-2016, 09:57 PM
  3. Wiring for Huanyang 220V 2.2kw VFD...NEED HELP PLEASE!
    By justindewoody in forum Spindles / VFD
    Last Post: 03-02-2016, 09:00 PM
  4. Replies: 8
    Last Post: 12-21-2014, 01:49 PM
  5. VFD Wiring from 220v Converter
    By TheProCreator in forum CNC Machine Related Electronics
    Last Post: 09-01-2010, 10:42 PM