Ok to try and start on the same page. I misspoke before The error I get is ER 09 or Power loss -"The frequency converter loses power and phase loss: the single phase and second phase (P00.20) are adjusted to 3"

This error occurs as soon as I plug the machine in. When I go to reset to factory parameters I don't think it is recognizing as i still get the ER09 after factory reset and if I go back to (P00.13) after changing to 10 and restarting it is back to 0 by itself.

Currently I have the wall power wired (black to R) (white to S)(Green to Ground) The manual says (R.S.T input terminal of AC line power (220V 380V class, for both single/three phase, single phase connected to any two)



Additionally I have my spindle has the fully shielded cable (grounded at one end only VFD side) and the 4th pin grounded at the spindle and back to the machines frame. Does this seem correct? I will can the manual I have and create a PDF. to pass along.