586,043 active members*
3,762 visitors online*
IndustryArena Forum > CNC Electronics > Spindles / VFD > HuanYang With 2.2Kw Air cooled spindle - how do I get a zero speed signal from it?
Results 1 to 12 of 12
    Apr 2005
    629
    Greetings.
    I am trying to figure out how to get a zero speed signal from the VFD so that I don't destroy my tool change system.
    It appears that parameter 50 when set to 3 provides this signal,
    I have checked for voltage differences between DRV and DCM and I have check for continuity changes between the same terminals, neither of which changed with the spindle running or stopped.
    Most probably I am doing something wrong or I don't know how to use that "output".
    Any help would be greatly appreciated!
    Chris D
    15362
    Re: HuanYang With 2.2Kw Air cooled spindle - how do I get a zero speed signal from it
    Quote Originally Posted by Chris D View Post
    Greetings.
    Chris D
    It will depend how you are controlling the VFD Drive
    PD050 may do what you want, depending on your VFD Drive model it may be 04 some are using 03 and or 04 for Zero speed you may also look at PD052 as you could use these relays also
    You won't measure anything, the For and DCM are just switched with a Relay normally
    DRV is an opto output you need a +24v / 100ma voltage to use these outputs ( Which can be supplied by the drive if it has a +24v )
    Mactec54
    Apr 2005
    629
    Hi
    How would I Wire that? My control uses 24v logic, but not sure how to wire this.
    Does that pull my signal low when activated?
    Chris
    15362
    Hi
    Chris
    Don't know what your control or Breakout Board is
    Mactec54
    Apr 2005
    629
    I'm using a centroid Acorn controller - no breakout boards needed.
    Chris
    Apr 2005
    629
    THis morning I got some time on the machine to figure this out. For my VFD, to get a "relay" type control signal, I used the FB & FC terminals and set parameter 52 to 2. Testing showed the contact operating when the spindle comes to a stop, not just at the STOP signal. This should do the trick for my needs.
    Chris D
    15362
    Chris D
    Acorn yes it has it's own Breakout Board most controls like this the Breakout Board is part of the package
    FB & FC is what most use, as it is the easiest to set up / use
    Mactec54
    24221
    The solid state outputs are just as easy to use, as long as the load is less than 24vdc @ 100ma, they are opto-isolated transistor sink, the At Zero Speed function is the one to use, it varies with model.
    What are the type of inputs on the Acorn, sink or source?
    Albert E.
    15362
    Acorn has some inputs H1 H4 that are sinking ( NPN ) which could be used
    There has been problems with the these output on the VFD Drive, it may be they never got connected correctly as why they where unreliable
    Mactec54
    24221
    It is too bad the transistor outputs have their commons connected, if each were brought out separately, they could be used in a sink or source manner.
    Albert E.
    15362
    According to the Acorn I/0 Map has sourcing
    Mactec54
    24221
    One note on the warning not to use two wire sensors would not apply in this case as a the Opto transistor outputs sink enough current, it applies to the 2 wire Prox type/versions.
    The Huanyang should interface OK.
    Albert E.
  1. Replies: 10
    Last Post: 12-22-2020, 10:15 AM
  2. Replies: 67
    Last Post: 07-29-2020, 02:22 PM
  3. Pulley min/max for Huanyang VFD and air cooled 2.2kw spindle
    By chrishallowell in forum Spindles / VFD
    Last Post: 12-14-2016, 02:39 PM
  4. Brand New 2.2KW (3HP) Air-cooled Spindle motor and 2.2KW VFD
    By automationtechinc in forum For Sale Only
    Last Post: 01-19-2015, 10:30 PM
