Looking for help setting parameters on a HY GT Series 5.5kW VFD driving a 1.5kW 220V 6A 24000rpm air-cooled spindle. I'd like to control the spindle speed from the pot knob on the keypad. I'm having 2 issues when while setting up:

1. With basic spindle parameters set, and pressing Run the spindle accelerates to about 7200rpm and frequency = 120hz (keypad reference frequency) , but turning POT knob has no effect.
2. Attempting to Auto-tune, the VFD accelerates to a constant frequency and after a minute or so, stops and shows EEP error.

My settings are:
P0.00 0
P0.01 0
P0.02 0
P0.03 400
P0.04 400
P0.05 120
P0.6 0
P0.07 0
P0.09 0
P0.10 0
P0.11 10
P0.12 10
P0.13 0
P0.14 6
P0.15 1
P0.16 0
P0.17 0

P1.00 0
P1.01 10
P1.02 0.0
P1.03 0.0
P1.04 0.0
P1.05 0
P1.06 0

P2.01 1.5
P2.02 400
P2.02 24000
P2.03 220
P2.04 6

Any ideas on what is wrong?