    Fanuc O-MC Alarm 405 "Z axis wrong (ZRN)"

    After a system software upgrade we recently had on two of our Mach 3 Horizontal Machining Centers, the Z axis forgets or loses its home position periodically. The upgrade was to add an option for programming, single direction positioning, and new EPROM chips (5). The home position gets "lost" after we shut down for the night and reboot the next morning. Batteries were just replaced in this machine also. Plus, if batteries were dead all the positions would be lost.
    Previous errors were adjusted for but never resolved as to why they occured. I believe before I worked here the previous guy just offset the parameter value of either/or 0510 and 0710. What else would control the machine home position? Is it necessary to adjust grid shift or the 710 ref. point value? The manual is not clear on the grid shift scale, I don't know if a 1 is .1" or .0001". They identify the inch and metric values for the 708-711 params but not the 508-511 ones.
    How can the machine forget or lose its Z axis home position by up to a few inches if the parameters aren't touched? No limit switch problems come up either. Anyone else have a suggestion?

  2. #2
    Join Date
    Dec 2003
    Posts
    24221
    The grid shift values are in 'Units of Detection' IOW detection counts/inch.
    The manual shows alarm 405 cause as 'axis card faulty'.
    Reference return is abnormal!.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Sep 2007
    Posts
    33
    In my manual it says 405 is "A position control error. Reference position return may have failed due to a problem in the NC or the servo system. Restart operations with manual reference position return."

    Solution:

    The manual was sort of right, although a normal manual reference return wouldn't work. I set bit 2 of parameter 0022 to 0 in order to "forget" the Z axis reference position. Powered down the machine. Powered back up and did a manual reference point return on Z axis and it found its original home position within .002". I plan to adjust the 0510 grid shift parameter to compensate for the .002".
    I still suspect a hardware/software issue somewhere since it should never lose its home position to begin with. I would suspect the axis card but both machines started doing this after Fanuc came out here and installed new EPROMs and options just 3 months ago. They will be coming out next week to go over the problem. I will post findings.

Similar Threads

  1. "Z" axis amp alarm
    By vista industria in forum Fadal
    Replies: 0
    Last Post: 09-06-2007, 02:47 AM
  2. Replies: 14
    Last Post: 01-08-2007, 06:10 AM
  3. "A" Axis Substitution Macro Programming For Fanuc
    By xleng in forum G-Code Programing
    Replies: 5
    Last Post: 12-08-2006, 08:52 PM
  4. Fanuc 18t Turret alarm "1110"
    By senna95 in forum Fanuc
    Replies: 0
    Last Post: 10-18-2006, 05:03 PM
  5. ALARM!!! "Commanded X Axis move too far / Positive"
    By aimeahz in forum Bridgeport / Hardinge Mills
    Replies: 6
    Last Post: 04-20-2006, 11:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •