Re: Breaker sizing for CNC cabinet (AC servos and VFD)
Originally Posted by
Titaniumboy
Time Current Coordination curves for thermal magnetic breakers behave differently than many people think they should.
For example, your Gladiator breaker will take between 8 seconds and 2 minutes to trip at 20 Amps. At 15 Amps it will take between 30 seconds and 10 minutes to trip.
It is much the same for Joe’s Potter Brumfield circuit breaker. At 20 Amps it will take between 2.2 seconds and 20 seconds to trip. At 15 Amps it will take between 4.5 seconds and 40 seconds to trip.
That's because a lot of people don't understand that circuit breakers are to protect the wire (not the component / appliance) and stop excessive current draw resulting in fires.
7xCNC.com - CNC info for the minilathe (7x10, 7x12, 7x14, 7x16)