the reason I chose 6A breakers is because they are a standard size therefore readily and cheaply available.
You can get 5A, 4A etc breakers but they are harder to find and more expensive.
https://nz.element14.com/eaton-cutle...tic/dp/1735725
https://nz.element14.com/eaton-heine...tic/dp/1704961
Well if 40A is the spec then it makes sense to use it. Just remember that 99% of the time it will draw just a few amps. I would suspect that a D curve breaker of 20A would be enough.
The breaker inside the cabinet is to protect the device, in this case a VFD. We do not want it to trip unnecessarily, but we do need it to trip to save the device....hopefully.
I think I would try a 20A or 25A D curve to start with. If you get no nuisance trips, all well and good, but if you do get nuisance trips then up the breaker until they stop, say 32A or 40A.
You should reserve some budget for line filters. VFD's and servo drives are renowned for being electrically noisy, and you should use either line reactors or at least two stage line filters
to try to prevent electrical noise from propagating from the VFD (servo drives) to other sensitive 230VAC powered devices like the PC. This sort of thing would be suitable for the VFD:
https://nz.element14.com/united-auto...36a/dp/3618172
Having one filter per servo drive would be nice, but gets expensive, so you'd probably get one 16A-20A line filter to do all three:
https://nz.element14.com/corcom-te-c...ase/dp/9586490