    Talking Toroidal transformer question

    I purchased a y236905 from avel lindberg.

    http://www.avellindberg.com/transfor...ange_specs.htm

    i am wondering about how to wire the primary's from my 115v source.
    I see for 115v ac that it seems the input should be wired as parralel,
    for 230v ac it should be wired in series.

    http://www.avellindberg.com/transfor...onnections.htm

    If my total applied ac voltage is 115v in series why would it show 230 v in
    the wiring dia. is it just the way the 2 seperate coils are wound that would
    make the applied 115v add up to 230v if wired in series?
    I obviously am missing something , if it has 2 primarys and a potential of
    115v is wired across the 2 coils in series the potential of 115v should not
    change ?
    what am i missing , besides my brains
    Dennis

  2. #2
    Join Date
    Jun 2007
    Posts
    3757

    Cool Specs?

    You are not missing anything. Just a bit of theory has gone, or never been.

    The link you gave only gave output specs for the transformer.
    These are only rough numbers, but it will help you understand.

    The next part assumes the output of the transformer is loaded to 800 watts.

    For 230v and 800w (Ignoring efficiency and resistive loss fudges by transformer designer)
    230 volts x 3.48 amps = 800 watts.

    for 115v applied
    115 volts x 6.96 amps = 800 watts.

    If you have 2 115v windings in series with 3.48 amps x (115 + 115) = 800w.
    now if you put the 115v windings in parallel and apply 115v
    The windings will be rated at about 3.5 amps.
    When you have 2 in parallel, the total current at 115v will be 3.48 + 3.48 = 6.96 amps.

    Now for some LIVE TESTING. No fingers connected at any time!
    Now lets assume there is no load on the transformer secondary.

    It is very important that the windings are phased correctly.

    For 230vAC
    When in series, then end of the one winding MUST go to the start of the other winding.

    For 115vAC
    When in parallel the starts are connected together, and the finishes are connected together.

    If you have a spec sheet which clearly says which wires to parallel for 115v or which wires to connect in series then follow the instructions.

    If the spec sheet shows a 230v connection, and shows the centre series connection, then one of those wires is a start of a winding, and the second is the end of the other winding.

    If you don't know which are the starts, and finishes, then you need carry out some tests.
    In the following S1 and F1 are winding 1 start and finish. S2 And F2 are winding 2.

    On 115v it is easy to test if the phasing is correct.
    1). If we don't know the start lets take one wire of each of the windings, and assume they are starts.
    2). Connect them together. S1/S2
    3). Connect 115v to S1/S2 and F1.
    4). Measure between F1 and F2 with a meter on ACv (> 200v).
    You should get very close to zero volts. If so go to step 6)
    5). If you get 230 volts then the assumption at 1) was WRONG. It was actually S1/F2.
    TURN OFF POWER
    If you get to here a second time CALL IN AN EXPERT. You will kill yourself. :nono:
    Make new assuption for S2, and go back to step 1)

    6). TURN OFF POWER.
    Connect F1 to F2, and apply power. Measure outputs. You should get 60V on each of the output windings.:cheers:
    Super X3. 3600rpm. Sheridan 6"x24" Lathe + more. Three ways to fix things: The right way, the other way, and maybe your way, which is possibly a faster wrong way.

  3. #3
    Join Date
    Jan 2005
    Posts
    126
    Hi neilw20,
    so if i am understanding this right , because it is rated at 800watts,
    that is what is to determine the primary wiring configuration ,
    at 115v / parralel / it will be able to handle over 6 amps, and at
    230v /series / it can handle half that,,,
    but what if , the primary's are wired in series and we connected 115v
    across them and the ratio of the transformer is 1:1 ,, would the output be
    115v but only able to handle half the transformers rated current ? The output
    couldn't be 230v in this instance ?

    Thanxs for your help
    Dennis

  4. #4
    Join Date
    Jun 2007
    Posts
    3757

    Post Take care.

    If you can't follow the steps I outline, you should get an electrician or elctronics person to explain what I have outlined.

    If you apply 115v in the 230v configuration, then your output windings will be only 50% of the design value. This will do no harm, but it might not do what you intended.

    If you email me your circuit diagram for what you are about to embark on I may be able to help further.
    As previously mentioned, the www link for the 800w transformer does not give it's full spec.
    Only output. It doesn't say what the input is/can be.

    Take care.
    Super X3. 3600rpm. Sheridan 6"x24" Lathe + more. Three ways to fix things: The right way, the other way, and maybe your way, which is possibly a faster wrong way.

  5. #5
    Join Date
    Jan 2005
    Posts
    126
    Thanks neilw20, I have the instructions for the exact wiring , and do not intend to wire it any differently than what is called for .
    I was only trying to see if I was missing something about the way transformers/coils work .
    thank you
    Dennis

Similar Threads

  1. How to wire a toroidal transformer..need advice
    By bgolash in forum CNC Machine Related Electronics
    Replies: 15
    Last Post: 11-13-2007, 03:22 AM
  2. toroidal transformer
    By cueshark in forum CNC Machine Related Electronics
    Replies: 1
    Last Post: 05-05-2007, 03:31 AM
  3. Question on lowering output voltage from a toroidal coil
    By southernexplore in forum CNC Machine Related Electronics
    Replies: 1
    Last Post: 07-26-2006, 09:18 PM
  4. Help with toroidal transformer
    By CAM_MAN in forum CNC Machine Related Electronics
    Replies: 7
    Last Post: 11-16-2005, 02:35 AM
  5. Help with Toroidal Transformer
    By bill south in forum CNC Machine Related Electronics
    Replies: 6
    Last Post: 08-02-2005, 08:40 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •